    Default tapping a steam boiler?

    Hi,
    I have an old steam boiler that I want to install an electronic Low Water Cut Off into. Unfortunately there is no opening in the side of the boiler where the probe can go. The probe requires a 3/4" NPT tap which would require a 29/32" hole. I imagine I can carefully drill the hole in the side of one of the sections and then cut the threads. What type of drill bit should be used to do this? I know I would use cutting oil to keep it from building up heat while drilling. Should it be drilled in increments of increasing size? Not sure if this is a terrible idea or if there are alternatives to get my LWCO installed with some kind of remote setup.

    The boiler is a 120,000 BTU natural gas Sears / Dunkirk that I believe was manufactured in 1979. Serial Number 7911104.

    Suggestions appreciated.

    Thanks!
    David Sorkin

  2. #2
    Plumbing Contractor for 49 years johnjh2o1's Avatar
    Join Date
    Aug 2009
    Location
    South*East
    Posts
    1,121

    Default

    If it is a steam boiler there should be a gauge glass. You can install a tee in the lower tapping for the glass and install your probe in it.

    John

  3. #3
    DIY Junior Member dsorkin's Avatar
    Join Date
    Jun 2010
    Location
    New Jersey
    Posts
    8

    Default

    Thanks for the reply John. I had also thought of doing that but wasn't sure if it would be safe enough. Do you know if that is a recognized installation method or if there was ever an inspector in my house they would get a good laugh at my expense from it? I like this idea because besides not having to drill a hole in the boiler it would also allow me to easily change the height of the probe if I need to make adjustments.

    Thanks!

    Here are some pictures, note probe in lower right of photo.



    Last edited by dsorkin; 06-03-2010 at 03:29 AM.

  4. #4
    DIY Junior Member dsorkin's Avatar
    Join Date
    Jun 2010
    Location
    New Jersey
    Posts
    8

    Default

    Follow up - I spoke with Hydrolevel (manufacturer of the LWCO) and they confirm the installation of the probe into the riser pipe.

    Many thanks!

Similar Threads

  1. indirect on old steam boiler
    By wallygater in forum Boiler Forum
    Replies: 10
    Last Post: 04-23-2010, 12:09 PM
  2. Replacing steam boiler
    By milk001 in forum Boiler Forum
    Replies: 14
    Last Post: 12-10-2009, 08:32 PM
  3. longevity of a steam boiler
    By dripdrip in forum Boiler Forum
    Replies: 0
    Last Post: 09-19-2009, 07:32 AM
  4. steam boiler
    By hids2000 in forum HVAC Heating & Cooling
    Replies: 2
    Last Post: 02-07-2007, 08:43 PM
  5. Utica steam boiler leaking????
    By harveymasons in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 8
    Last Post: 09-29-2005, 08:13 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •