Thread: priming 3" floor drain, Canada

  1. #1
    Plumber Esquire's Avatar
    Join Date
    Nov 2009
    Location
    Newfoundland
    Posts
    65

    Default priming 3" floor drain, Canada

    I'm thinking about moving my HWT to another room in the house. I was going to just bust up the concrete and put in a 3" P-trap and bit of pipe and then cut off the pipe flush to the new floor and put a floor drain grate on it. My question is, if you guys had just 3" ABS how about you trap seal prime this drain without using an indirect connection priming from above?

    I know if I buy actually floor drains (which would cost more) they would have female connectiotns on them from the manufacturer for adding a primer line.

  2. #2
    Journeyman & Gas Fitter Doherty Plumbing's Avatar
    Join Date
    Jun 2009
    Location
    Penticton, BC
    Posts
    810

    Default

    Quote Originally Posted by Esquire View Post
    I'm thinking about moving my HWT to another room in the house. I was going to just bust up the concrete and put in a 3" P-trap and bit of pipe and then cut off the pipe flush to the new floor and put a floor drain grate on it. My question is, if you guys had just 3" ABS how about you trap seal prime this drain without using an indirect connection priming from above?

    I know if I buy actually floor drains (which would cost more) they would have female connectiotns on them from the manufacturer for adding a primer line.
    You are allowed to drill the connection for the trap primer into the HUB of the floor drain above the trap seal. Then thread in a 1/4" male by compression fitting.

    You are allowed to do this because the trap primer itself should have an air gap.

  3. #3
    Plumber Esquire's Avatar
    Join Date
    Nov 2009
    Location
    Newfoundland
    Posts
    65

    Default

    What tools and fittings would you use to tap into abs? I don't think I've actually seen it done. I've seen the finished product in the feild but never witnessed to doing of it.

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default

    A drill bit and a pipe thread tap. Or use a tee in the vertical pipe with the proper sized bushing(s) into it. How you make the connection is NOT as important and HOW you supply the water to the trap.

  5. #5
    Journeyman & Gas Fitter Doherty Plumbing's Avatar
    Join Date
    Jun 2009
    Location
    Penticton, BC
    Posts
    810

    Default

    Quote Originally Posted by Esquire View Post
    What tools and fittings would you use to tap into abs? I don't think I've actually seen it done. I've seen the finished product in the feild but never witnessed to doing of it.
    I simply drill out the ABS with a drill bit that is just a bit smaller then the size of the fitting. Then very carefully just start threading in the fitting. It should carve it's own threads, but just becareful to not cross thread it! But if you have a tap set like HJ suggested then that's a good way to do it too!

  6. #6
    DIY Member christoff's Avatar
    Join Date
    Dec 2007
    Location
    Toronto Canada
    Posts
    49

    Default

    does the primer line have to be in a sleeve, or can it just be placed into the gravel when put under the floor, im am doing that right now

  7. #7
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default

    Direct buried.

  8. #8
    DIY Member benze's Avatar
    Join Date
    Aug 2010
    Location
    Montreal, Canada
    Posts
    63

    Default

    Quote Originally Posted by Doherty Plumbing View Post
    You are allowed to drill the connection for the trap primer into the HUB of the floor drain above the trap seal. Then thread in a 1/4" male by compression fitting.

    You are allowed to do this because the trap primer itself should have an air gap.
    You wouldn't by any chance have a picture of a setup like this by any chance? I'm in the process of doing the same thing and would love to see a setup before I attempt one myself.

    What size primer line is recommended? 1/2"?

    Thanks,

    Eric

  9. #9
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default

    1/2" usually because it is a gravity drain and too small a pipe, might cause overflow at the primer, depending on the volume of water it releases.

Similar Threads

  1. floor drain, Canada
    By christoff in forum Canadian Plumbing Code Questions
    Replies: 6
    Last Post: 06-20-2010, 04:48 AM
  2. floor drain, Canada
    By christoff in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 06-20-2010, 04:48 AM
  3. trap primer for the floor drain, Canada
    By simmy1919 in forum Canadian Plumbing Code Questions
    Replies: 2
    Last Post: 06-02-2010, 07:31 PM
  4. trap primer for the floor drain, Canada
    By simmy1919 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 06-02-2010, 07:31 PM
  5. Is 1 1/2" drain pipe ok for shower drain? and 2nd floor P-trap question...
    By paule123 in forum Shower & bathtub Forum & Blog
    Replies: 1
    Last Post: 06-12-2005, 10:15 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •