Condensate Pump tie into DWV

Users who are viewing this thread

Lakee911

I&C Engineer (mostly WWTP)
Messages
1,254
Reaction score
1
Points
0
Location
Columbus, OH
Hi all,
Curious to see what you guys recomend for using DWV for drain for a condensate pump. Is this the correct procedure? Condensate Pump Drain to air gap to P trap to DWV system? Any better ideas? Air gap needed? If Condensate drain (from A/C) has a trap, do I still need the airgap and trap after the pump?

Thx
Jason
 

hj

Master Plumber
Messages
33,602
Reaction score
1,041
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
pump

The pump makes the condensate connection from the AC an indirect connection so it does not need a trap. The pump should have a check valve on its discharge connection, so you can make any type of connection to the DWV that will work.
 