IF the arm slopes enough so the connection to the vertical pipe is below the weir of the trap, it WILL create a partial "S" trap, but whether it automatically causes siphonage depends on whether the flow is adequate to fill the pipe. The minimum length requirement has NOTHING to do with it becoming an "S" trap, and I have NEVER had an inspector fail an installation because the trap was "fitting to fitting" with the tee. The length of the tee's branch, plus the distance from the end of the bell to the downward facing elbow, is almost the 4" distance anyway, regardless of how long the pipe piece is.