    Default Basement Sump Pump Siphoning & Air-locking

    I have a basement sump pump which operates as it is suppose to. The pump operates till the water level drops and the float switch kicks the pump off. But at this point the outgoing water effectively siphons the remaining water out of the sump causing the pump to become air-locked. After becoming air-locked, once the sump has filled the pump will run continually for days without pumping any water.

    I'd like to know if there is a anti-siphon valve I can put in this system to stop this from happening. Alternately I've also been thinking about drilling a hole in the discharge line above the pump but before the check valve.....Just wondering if this is allowed by code.

    Any suggestions would be greatly appreciated.

    Thanks

  2. #2
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,161

    Default

    The pumps I have dealt with (Zoeller) included instructions to put a small hole in the discharge pipe in the crock between the pump and check valve.

  3. #3
    Journeyman & Gas Fitter Doherty Plumbing's Avatar
    Join Date
    Jun 2009
    Location
    Penticton, BC
    Posts
    810

    Default

    Quote Originally Posted by jasonw83 View Post
    I have a basement sump pump which operates as it is suppose to. The pump operates till the water level drops and the float switch kicks the pump off. But at this point the outgoing water effectively siphons the remaining water out of the sump causing the pump to become air-locked. After becoming air-locked, once the sump has filled the pump will run continually for days without pumping any water.

    I'd like to know if there is a anti-siphon valve I can put in this system to stop this from happening. Alternately I've also been thinking about drilling a hole in the discharge line above the pump but before the check valve.....Just wondering if this is allowed by code.

    Any suggestions would be greatly appreciated.

    Thanks
    I doubt code would have anything to say at all about drilling a hole in the discharge of the pump. It's done all the time......

    You could also try leaving more water in the sump when you pump it out.

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,687

    Default

    There is NO WAY to leave more water in the pit if it is being siphoned out. IT will siphon until ALL the water is gone and the system sucks water or the water level in the pit drops to the elevation of the pipe's outlet. A hole in the pipe will allow the air trap to be evacuated as water fills the pit. If the pump is running without pumping water, your shaft seal is probably damaged and you will need a new pump shortly.

Similar Threads

  1. Basement Systems Inc. Triple Safe Sump Pump
    By derekgaddy in forum Pumps and Tanks Well Forum & Blog
    Replies: 7
    Last Post: 02-17-2010, 11:22 AM
  2. Sump Pump in basement not working
    By rickracko in forum Pumps and Tanks Well Forum & Blog
    Replies: 0
    Last Post: 11-22-2009, 11:41 AM
  3. Basement sump pump smell
    By MattN03 in forum Pumps and Tanks Well Forum & Blog
    Replies: 4
    Last Post: 04-16-2008, 04:58 PM
  4. Basement finishing with no sump pump: do I need one?
    By vdecker in forum Pumps and Tanks Well Forum & Blog
    Replies: 2
    Last Post: 08-12-2007, 04:46 AM
  5. Basement laundry tub - sump+pump or pump-only?
    By whatever in forum Pumps and Tanks Well Forum & Blog
    Replies: 9
    Last Post: 03-21-2006, 09:18 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •