Thread: Possible wiring fault

  1. #1
    DIY Junior Member Mitch60's Avatar
    Join Date
    May 2010
    Location
    Prescott, AZ
    Posts
    8

    Default Possible wiring fault

    I have an office with computer equipment and I use a UPS (uninterruptible power supply) to prevent damage to the equipment and prevent data loss. On the back of the UPS is an LED that indicates wiring faults in the building. This LED lights (indicating a fault) up when load increases and can be anywhere from completely off to bright, depending on the number of appliances in use at the time on the circuit. This is the second UPS to indicate a wiring fault on this circuit. Appliances on the same circuit but not plugged into the UPS can also cause it to light up. The circuit seems to be wired with 14 gauge wiring, and the run to this room is probably around 100 feet.

    I've also purchased one of those fairly inexpensive plug-in, LED, wire fault testers at my local hardware store. This device does not register a fault, even when the LED on the UPS is registering one. I've used the same UPS on other circuits in the house and they do not show a fault.

    I'm wondering what this is indicating and if it can cause problems with my equipment.

    Thanks for any advice you can give me

  2. #2

    Default

    From what you describe its probably low voltage condition. The greater the load on a circuit the more the voltage drops. You need to use a multimeter to determine what the voltage is on that circuit when nothing is turned on. Connect the multimeter to a wall outlet on that circuit - not to the UPS outlets. It should be around 120 volts. Then measure the voltage again when the fault light is on. If the voltage is below 115 volts the fault light is most likely caused by the voltage drop.

    Low voltage can be a real problem, however most consumer electronics will tolerate voltages as low as 110 volts. Your UPS will cut over to batteries if the voltage falls too much so you don't have to worry about anything plugged into the UPS. Fixing a low voltage condition can be complicated. It can be anything from a loose connection on the back of an outlet to a problem with the transformer at the street.

    -rick
    Last edited by drick; 05-19-2010 at 08:43 PM.

  3. #3
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,382

    Default

    You might want to call the UPS manufacturer or scour the manual to see if they can describe what can cause that indicator to turn on in more detail. You might also want to measure to see if you have any voltage between neutral and ground. On the UPS units I've played with, there is a dedicated indicator that shows if the incoming voltage is too low, and it is switching to the battery backup. Now, some of the better UPS devices actually run off the batteries, and don't actually switch. The line voltage just keeps the batteries charged rather than powering the a/c output circuits all of the time except when line in gets low.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  4. #4
    DIY Junior Member Mitch60's Avatar
    Join Date
    May 2010
    Location
    Prescott, AZ
    Posts
    8

    Default

    Quote Originally Posted by drick View Post
    From what you describe its probably low voltage condition. The greater the load on a circuit the more the voltage drops. You need to use a multimeter to determine what the voltage is on that circuit when nothing is turned on. Connect the multimeter to a wall outlet on that circuit - not to the UPS outlets. It should be around 120 volts. Then measure the voltage again when the fault light is on. If the voltage is below 115 volts the fault light is most likely caused by the voltage drop.

    Low voltage can be a real problem, however most consumer electronics will tolerate voltages as low as 110 volts. Your UPS will cut over to batteries if the voltage falls too much so you don't have to worry about anything plugged into the UPS. Fixing a low voltage condition can be complicated. It can be anything from a loose connection on the back of an outlet to a problem with the transformer at the street.

    -rick
    Thanks for the advice Rick

    I have several devices in the room running at the moment and the LED is glowing quite brightly. I checked the voltage (with my multi-meter) on several other outlets in the room and they are all averaging around 121v. The UPS also has a voltage-in meter built into the device and it's registering 120v. I also checked the voltage in my bathroom (which is a different circuit) and it's registering 123v. There is a slight voltage difference between the outlet the UPS is plugged into 120.5 +/- .3 and the other outlets in the room 121.5 +/- .3.

    This doesn't seem to indicate a low voltage condition, does it?

  5. #5
    DIY Junior Member Mitch60's Avatar
    Join Date
    May 2010
    Location
    Prescott, AZ
    Posts
    8

    Default

    Quote Originally Posted by jadnashua View Post
    You might want to call the UPS manufacturer or scour the manual to see if they can describe what can cause that indicator to turn on in more detail. You might also want to measure to see if you have any voltage between neutral and ground. On the UPS units I've played with, there is a dedicated indicator that shows if the incoming voltage is too low, and it is switching to the battery backup. Now, some of the better UPS devices actually run off the batteries, and don't actually switch. The line voltage just keeps the batteries charged rather than powering the a/c output circuits all of the time except when line in gets low.
    Thanks for the responce Jim

    I actually did call the UPS manufacture about this issue several weeks ago and they decided it was a defective unit, which they replaced. The new unit is sadly behaving the same. I measured the voltage between neutral and the ground as you suggested and it's registering .81v to 1.v. I measured some other circuits in the house and they're measuring no voltage neutral to ground.

    This seems like it might indicate something

  6. #6
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,382

    Default

    You still need to try to find out what that LED indicator is designed to represent. If the UPS is unplugged, and you check that recepticle, is there any voltage between the neutral and ground? If so, and you have none elsewhere, something's weird and needs to be investigated in the wiring.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  7. #7
    DIY Junior Member Mitch60's Avatar
    Join Date
    May 2010
    Location
    Prescott, AZ
    Posts
    8

    Default

    Quote Originally Posted by jadnashua View Post
    You still need to try to find out what that LED indicator is designed to represent. If the UPS is unplugged, and you check that recepticle, is there any voltage between the neutral and ground? If so, and you have none elsewhere, something's weird and needs to be investigated in the wiring.
    This is what the APC website has to say about the wire fault LED indicator. Not sure if this information is specific enough.

    Quote Originally Posted by APC
    Site Wiring Fault or Building Wiring Fault Indicator LED is on

    The Site Wiring Fault LED light is only present on 120V UPS and Surge products. On APC UPS products this indicator is typically on the rear panel. The purpose of this indicator light is to warn you that there are problems with your building wiring that may result in a shock hazard.

    APC recommends that you have a qualified electrician inspect your wiring for one or more of the conditions listed below.

    Reasons why the Site Wiring LED light will illuminate:

    1. Overloaded neutral wire (>5vdc measured between Neutral and Ground).

    2. Reversed polarity (hot and neutral wires are reversed).

    3. Missing ground wire. (Note: this also includes using a 3 prong to 2 prong adapter)

    If the outlet that the APC UPS unit is plugged into is not properly grounded or properly wired, the unit will attempt to absorb the excess voltage instead of redirect it to ground. It would be like attempting to catch a bullet with a catcher mit, where as if the light is not on it would be able to redirect the excess voltage to ground. Therefore, in order to maintain your warranty and protection under APC's Equipment Protection Policy, be sure that the APC unit is only plugged into a properly grounded outlet where the Site Wiring Fault Indicator (SWFI) light is not illuminated.
    I notice the "overloaded neutral wire" indicates a problem if there is >5vdc (not ac) detected. I tried to measure the voltage in dc, neutral to ground, and the reading fluctuates wildly in millavolts between
    -100mv to -200mv

    I just unplugged the UPS from the circuit and the extra voltage measured in ac with it plugged in is reduced to .4vac from about .8vac with it plugged in. Perhaps my next step should be to call APC again... hmmmm

  8. #8

    Default

    I think they ment to say >5vac. There is no dc voltage to measure.

    "Overloaded neutral" is an odd way of stating what the problem is. What you *might* have is a high resistance neutral. Generally this is caused by a poor quality splice or backstabbed outlets and switches (as opposed to wrapping the wire around the screw terminal). When this occurs the ground wire has a lower resistance back to the breaker panel than the nutral wire. Under normal situaions the resistance between the two wires is the same (almost 0) so no voltage can be measured between them. If you have a high resistance neutral the more power you use the larger the voltage reading will be between neutral and ground. If you turn off everything on that circuit it will return to 0V.

    If you do have a high resistance neutral fixing it can be a PITA as it can be caused by various things in the circuit. Hmm, turn the power to that circuit off and remove the outlet the surge protector is plugged into. Are the wires to the outles wrapped around the screws or backstabbed? Also what is the approximate age of the house and wiring?

    Also are you sure the other outlets on other circuits in the house read 0V between neurtal and ground?
    -rick

  9. #9
    DIY Junior Member Mitch60's Avatar
    Join Date
    May 2010
    Location
    Prescott, AZ
    Posts
    8

    Default

    Something new:

    I decided to check another circuit for nuetral to ground voltage with and without load. It measured .05vac with minimal load, and .125vac with more load. This seems consistant with the circuit with the UPS, in other words, more load more current across the nuetral/ground. I now believe this is what the LED on the UPS is indicating. With minimal load on the circuit the LED is off, as the load increases, the LEDs brightness increases.

  10. #10
    DIY Junior Member Mitch60's Avatar
    Join Date
    May 2010
    Location
    Prescott, AZ
    Posts
    8

    Default

    Quote Originally Posted by drick
    If you do have a high resistance neutral fixing it can be a PITA as it can be caused by various things in the circuit. Hmm, turn the power to that circuit off and remove the outlet the surge protector is plugged into. Are the wires to the outles wrapped around the screws or backstabbed? Also what is the approximate age of the house and wiring?

    I'm fairly certian the outlets are "backstabed", but I'd have to pull one to check for sure. The house and wiring is about 7-years-old.

    Edit: The outlets are definitely backstabbed and NOT wrapped. Isn't this typical procedure nowadays?
    Last edited by Mitch60; 05-20-2010 at 07:47 PM.

  11. #11
    DIY Junior Member Mitch60's Avatar
    Join Date
    May 2010
    Location
    Prescott, AZ
    Posts
    8

    Default

    Quote Originally Posted by drick
    Also are you sure the other outlets on other circuits in the house read 0V between neurtal and ground?
    Actually no, they are all registering varying amounts of voltage (neutral to ground)dependant upon load. I mistook the original .05vac as no load, thinking it might be an error with my multi-meter.

  12. #12

    Default

    Quote Originally Posted by Mitch60 View Post
    I'm fairly certian the outlets are "backstabed", but I'd have to pull one to check for sure. The house and wiring is about 7-years-old.

    Edit: The outlets are definitely backstabbed and NOT wrapped. Isn't this typical procedure nowadays?
    Its not unusual. However if I was looking to fix a high resistance issue the first thing I would do would be change the outlets and switches from backstabbed to wrapped connections. It provides a larger contact area and IMO improves the integrity of the connections. I'd also check any wire nutted nutral connections containing 3 or more wires in any box that contained a switch.

    You can possibly narrow your seach a bit. If the outlet the UPS is connected to has 2 black and 2 white wires individually cap all the wires, and turn that circuit back on. Only the remaining lights and outlets that have power are the ones you are interested in checking. All the others are upstream of that outlet and have no effect on the path the neutral wire takes back to the breaker panel.

    -rick

  13. #13
    DIY Junior Member Mitch60's Avatar
    Join Date
    May 2010
    Location
    Prescott, AZ
    Posts
    8

    Default

    Quote Originally Posted by drick View Post
    Its not unusual. However if I was looking to fix a high resistance issue the first thing I would do would be change the outlets and switches from backstabbed to wrapped connections. It provides a larger contact area and IMO improves the integrity of the connections. I'd also check any wire nutted nutral connections containing 3 or more wires in any box that contained a switch.

    You can possibly narrow your seach a bit. If the outlet the UPS is connected to has 2 black and 2 white wires individually cap all the wires, and turn that circuit back on. Only the remaining lights and outlets that have power are the ones you are interested in checking. All the others are upstream of that outlet and have no effect on the path the neutral wire takes back to the breaker panel.

    -rick
    This seems like great advice Rick, especially the part about determining outlets upstream from the UPS outlet. I'm fairly certain all the switches/lightning are on a different circuit from the outlets, so I shouldn't have any problems there. I've done lots of wiring so this shouldn't be a problem for me to handle, only the time involved; I'll probably get to it tomorrow or over the weekend. I'll post back with the results.

    Thanks again for all the help.

  14. #14
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,382

    Default

    I don't like the spring-loaded, back-stabbed outlet connections. There are some that you can insert in the back and there's a screw clamp that tightens them down - those are fine. Especially if that receptacle gets a high load, the less than ideal contact of a back-stabbed unit means heat, and over time and cycling, the spring tension can decrease, making it worse.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  15. #15

    Default

    I'm wondering what this is indicating and if it can cause problems with my equipment.
    I have no idea but............................ I'M HEADED TO PRESCOTT IN A FEW MINUTES!! (Friday afternoon)