Thread: Surge protector placement

  1. #1
    Senior Robin Hood Guy Ian Gills's Avatar
    Join Date
    Jul 2007
    Location
    USA
    Posts
    2,781

    Default Surge protector placement

    I have just noticed in my new Square D panel that the "breaker type" surge protector has been placed about half way down i.e. not in the top two breaker places.

    Does this matter? I understand that for optimal performance a surge protector should be wired as close to the bus bar as possible. Is there anything wrong with what my electrician has done?

    Thanks.

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default

    All the breaker positions fasten to the bus bar. A surge would be "instanteous" along the entire bus, and your protector should drain it off equally well regardless of its location in the panel.

  3. #3
    Senior Robin Hood Guy Ian Gills's Avatar
    Join Date
    Jul 2007
    Location
    USA
    Posts
    2,781

    Default

    Thank you hj.