Installing Cutler Hammer Surge Protector

Users who are viewing this thread

basketboy

New Member
Messages
2
Reaction score
0
Points
0
Location
Pennsylvania
I bought a Cutler Hammer CHSPULTRA whole house surge protection device, which comes with 4 wires: two go to a 2-pole breaker, one that goes to the neutral bus bar and the fourth wire that is meant to go to the ground bus bar. My load center does not have a separate ground bus bar. Any idea if both wires can be wired to the neutral bus bar or do I need to have a separate ground bar installed? Cutler Hammer's website was no help. Thanks in advance for any suggestions.
 

Ian Gills

Senior Robin Hood Guy
Messages
2,743
Reaction score
3
Points
0
Location
USA
If this is the main service panel, then yes they can, but make sure they go under seperate lugs.
 

basketboy

New Member
Messages
2
Reaction score
0
Points
0
Location
Pennsylvania
Thanks for the reply. It was the main service panel so I did as you suggested. Surge protector is up and running.
 

Ian Gills

Senior Robin Hood Guy
Messages
2,743
Reaction score
3
Points
0
Location
USA
Given through those are where any surge will end up, I still think two are better than one.
 