    Im remodeling and have 1 bathrrom above the other, Im going to use 3/4 copper and was wondering whats the best way to go about it so 2 people camn shower at the same time (In different showers) with out a huge drop in pressure...thanks

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,412

    Default

    Unless you are using multiple heads in the shower, 3/4" lines up to the valve (you can reduce then to 1/2" to save some money) should be fine.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    DIY Junior Member lakeport's Avatar
    Join Date
    May 2010
    Location
    waterloo
    Posts
    2

    Default

    thanks for the reply....so I should run 3/4 to the 1st shower then continue to the 2nd(branch off) or run 2 different 3/4 lines and t off ..thanks

  4. #4
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,412

    Default

    I'd run a 3/4" line and convert to 1/2" at each valve individually. A 3/4" line should be able to safely handle nearly 15gpm. A single shower head is maxed out at 2.5gpm per code (but allows multiple heads). A 1/2" valve should be able to handle in the range of 5gpm, so won't starve a single showerhead. As long as you T off the 3/4" line with individual 1/2" feeds to your valves, it should be fine unless you pressure is really subpar to begin with.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  5. #5
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default

    3/4 to the first and continue with 1/2" to the second will be more than adequate. Any HUGE drop in pressure will be because of inadequate piping TO that point.