Thread: Connecting #6 conductors

  1. #1
    DIY Member JAR8832's Avatar
    Join Date
    Feb 2008
    Location
    Wisconsin
    Posts
    98

    Default Connecting #6 conductors

    I need to connect (2) #6 conductors, but the largest wire nut I can find will only handle (1) #6 with (1) #8. Does such a wirenut exist or do I have to use something else? TIA

  2. #2
    DIY Member Lightwave's Avatar
    Join Date
    Aug 2007
    Location
    Vancouver, BC
    Posts
    98

    Default

    There are wirenuts for #6 wire. Keep looking.

    edit: Ideal part 30-454 is what you want.
    Last edited by Lightwave; 05-09-2010 at 02:38 PM.

  3. #3
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,651

    Default

    For the load you must have, I would prefer "Bundy lugs" or similar which clamp the wires together, and then tape over them.

  4. #4
    DIY Member JAR8832's Avatar
    Join Date
    Feb 2008
    Location
    Wisconsin
    Posts
    98

    Default

    Thanks for the info, I had to try a different store and they had the correct wire nuts. It's for a hot tub neutral in a service disconnect box (GFCI breaker is in main panel).