If you want a rough value is trying to maintain area, you can do it this way:
A=pi*r^2 or (pi*D^2)/4
Since pi and everything else in the equation is constant (except for r/D), double the diameter (or radius) equals 4x the area.
So four 1" pipes is roughly equal to a single 2" pipe.
If you want to find exact areas, you would look up the i.d. of the pipe(s) you are using and calculate the areas. This way is better especially if you are mixing different materials (PVC, PEX, copper, etc.) since some are IPS based and others are CTS based in how their nominal sizes are determined. In addition, wall thickness can vary between different materials. For instance, copper and CPVC are both measured based on CTS (Copper Tube Size), but a given size copper pipe has more flow area than the same size in CPVC since the copper walls are much thinner.
For something like this, you will not have to match the area, though. I suspect that your flowrate will be fairly low (normal for solar to pickup the temperature rise). Eventhough it would take 4 1" pipes to equal a 2" pipe in terms of area, you might be better off using four 3/4" lines (or less) instead.
Do you know what your pump can flow and at what level of head can it hit this flow?