I have four 1-1/2" vent pipes in my attic that I would like to combine into a single exit through the roof. What size should that pipe be, or how should I do it?

Do the pipe sizes need to increase as they are combined (as with drain pipes)?

Thanks
 

Shacko

Master Plumber-Gas Fitter
Messages
559
Reaction score
1
Points
0
Location
Rosedale, Md
You can combine them into one 2in. vent. Do you have a larger vent in that area? if so you can run them into that if it's 3in. or larger.
 

Winslow

Plumber
Messages
445
Reaction score
0
Points
0
Location
Hawaii
you can join them all together but the size after joining depends on what is attached to the individual vents, depending on which code you are under. According to the UPC you can join them all together under a 2" vent as long as the overall fixture units do not exceed 24.
 