sealing gas pipe threads ?

Users who are viewing this thread

Fabricator

Member
Messages
64
Reaction score
0
Points
6
Location
Illinois
hello. sorry for such a newbe question. but i have never messed with gas pipes. my hwh started leaking. so i am about to replace it. it is natural gas. is plumbers putty good for the threads ? if not, what ?

if there is anything you would like to add to a first time 40gl gas hwh swapper ?!


thanx
 

hj

Master Plumber
Messages
33,602
Reaction score
1,039
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
One word of advice, "Do not depend on the original installation to meet current installation requirements". You cannot always put the new one in just like the old one was, and if you think plumber's putty is a proper thread sealant for ANYTHING, especially gas, then you have NOT done much piping.
 

Fabricator

Member
Messages
64
Reaction score
0
Points
6
Location
Illinois
One word of advice, "Do not depend on the original installation to meet current installation requirements". You cannot always put the new one in just like the old one was, and if you think plumber's putty is a proper thread sealant for ANYTHING, especially gas, then you have NOT done much piping.


yeah. i can't count the # of code violations i have had to repair from the builder. i think the code officer was in the pockets of the builder.

ok, then what should i use ? i forgot to get a pan when i baught the richmond hwh yesterday. so i have to go to HD anyway.

thanx
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
Back to the question>>> plumbers putty is never used on threads of any kind. PIPE DOPE, also called pipe thread paste, is what to use. Great White, Megaloc, Rectorseal Tplus2, are some good ones.
 

Shacko

Master Plumber-Gas Fitter
Messages
559
Reaction score
1
Points
0
Location
Rosedale, Md
Don't forget to use a soapy water solution on the gas pipes when you turn the gas back on, we want zero leaks
 

Fabricator

Member
Messages
64
Reaction score
0
Points
6
Location
Illinois
thanx guys.

WH is in. i put a pan/drain in.


i flushed the living poop out of it. i would say at least 100 gallons.
i used Tplus2.
i soaped up the joints. no leaks.
and new dielectric fittings and a new shut off valve.


idk what kind of sealer the builder used. but it sure looked like plumbers puddy.


i have another question. on the in/out fittings of the WH. there is a blue plastic gasket (for lack of a better term). what is that for ?

thanx
 
Last edited:

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
If you are talking about the nipples that often come pre-attached to the water heater, the blue is a plastic dielectric lining to prevent corrosion of the outlet fitting.
 

Fabricator

Member
Messages
64
Reaction score
0
Points
6
Location
Illinois
yes, the pre-attatched nipples. i looked down in these nipples. there looked to be some kind of valveage down there about 2"s. what is that for ?

thanx guys :)
 