    Default What exactly is the inspector looking for?

    What are the exact things that an inspector will check upon viewing the completed plumbing. Will the inspector always require a pressure test for replacement of old pipes?

  2. #2
    DIY Senior Member plumguy's Avatar
    Join Date
    Jul 2005
    Location
    MA
    Posts
    192

    Default

    It all depends on the inspector and the amount of pipe replaced. But a normal test would be 125psi on water and 5psi on drains.

  3. #3
    DIY Senior Member plumguy's Avatar
    Join Date
    Jul 2005
    Location
    MA
    Posts
    192

    Default

    The inspector will also look for proper install by code and from reading you're other post... if you decide to use the cleanout as means of tying into the system expect to be failed.

  4. #4
    Tradesman Plumber Kristi's Avatar
    Join Date
    Jan 2005
    Location
    Vancouver, BC
    Posts
    176

    Default

    They'll be checking to make sure it's all installed up to code! Up here (Vancouver, BC) there's no short 90's in the drainage, no S-traps, the piping should drain downhill the whole way 1/4" per foot, proper venting, etc, ettc... it's really up to the individual inspector. Your local code is the best source of info, but isn't fun to navigate if you're not used to it. My inspectors usually let me get away without pressure testing drainage, but if you're a DIY homeowner, they will probably require one.

  5. #5
    Tradesman Plumber Kristi's Avatar
    Join Date
    Jan 2005
    Location
    Vancouver, BC
    Posts
    176

    Default

    lol... I just realized the same Plumguy!

  6. #6

    Default

    The inspector will also look for proper install by code and from reading you're other post... if you decide to use the cleanout as means of tying into the system expect to be failed.
    I was just curious why it wouldn't be allowed. I wasn't planning on doing it, I just want to understand why...the more I know the better my work will be in the long run

  7. #7
    DIY Senior Member plumguy's Avatar
    Join Date
    Jul 2005
    Location
    MA
    Posts
    192

    Default

    I think HJ explained it...it is not an approved fitting. A cleanout is not a wye it is a T and therefore is illegal. It is appreciated that you would replace it with another cleanout above..but because of the T design it can disrupt the flow of the drain and therefore is not allowed for the connection of a drain.

  8. #8

    Default

    I seem to missing something here, cause I just can't seem to wrap my head around the explanation. The cleanout in my system looks like this:

    Y

    not

    T

    I can understand why a T design would not be code, because water flows downhill and Ts are only only for vents, but I'm confused why a Y design would violate code.

    I appreciate those of you who are kind enough to help me out, as I am interested in learning as much as I can so I can do things right.