    Default Plenum Supply Mathematics: Volume vs Area

    Hello Everyone,

    I am upgrading my 2-ton HVAC system, installing a new A/C condenser and coil, but keeping the existing furnace and air handler. All are made by Rheem/Ruud. My furnace / air handler is in my basement in an updraft configuration. The basement ceiling is low (about 6 ft.). In the old configuration, there was an uncased evap coil boxed in with sheet metal sitting on top of the air handler. Above that was a custom-fabricated sheet metal supply plenum chamber that measured 18" x 31" x 8" (4464 sq. in). There were 4 outlets in this chamber to which four 7" diameter steel ducts connected; each duct leads to one of the four rooms in my house (house is 107 year old)

    Problem: the new evaporator coil, which is in a factory case, is too tall to match the existing plenum chamber. I'd like to use it "cased" as opposed to un-casing it and opening a whole new can of worms (even uncased, the coil doesn't quite fit in the old ductwork, but the case fits perfectly atop my air handler in terms of height and depth).

    When I place the new cased coil on top of my air handler, I'm left with only 5.75 inches of space between the top of the cased coil and the bottom of the floor joists to distribute the airflow to the four 7" ducts.

    I can fabricate a new supply plenum chamber that will fit, but, I'm not certain about the math. (Please see the attached diagram). The new supply plenum chamber will have the same VOLUME as the old one, but, it will reduce the height and width of the plenum duct (the area of a slice of the plenum, if that makes sense) to an area that is smaller than that of the cased evap coil (the plenum would be 5.75 x 40 = 230 sq in, and the cased coil is 17 x 21 = 357 sq in.).

    I'm concerned that I may create a venturi, forcing air through a space that it too small, creating a backlash that may reduce the efficiency and lifespan of the blower motor in my air handler.

    I appreciate anyone's advice on the attached diagram. If the diagram does not show up in this posting, you can see it at http://www.masterkeyhost.com/will/plenum_diagram.gif



    Thanks!
    Will
    Last edited by homewrecker2010; 04-20-2010 at 07:45 PM.

  2. #2
    DIY Member Lightwave's Avatar
    Join Date
    Aug 2007
    Location
    Vancouver, BC
    Posts
    98

    Default

    I'm far from an expert on ducting, but I'm pretty sure a 5.75" high plenum will not work. Air velocities in the 5.75" area will be high enough to cause severe noise issues and the backpressure could be too much for the blower to handle. I'd suggest either:

    1. Reframing the floor joists to create an opening for a taller plenum.

    2. Extending the plenum parallel to the floor joists--inside a joist bay--and connect your 7" ducts to the underside of the extended plenum.

    3. Converting your AHU to horizontal mount or replacing it with a horizontally mounted AHU.

    I don't know which of these options will work best. Consulting an engineer with experience in CFD for ducting might be in order.

  3. #3
    DIY Junior Member homewrecker2010's Avatar
    Join Date
    Apr 2010
    Location
    Saint Louis, Missouri
    Posts
    2

    Default

    Lightwave,

    Thanks very much for your input. Option #2, placing the plenum inside the joist bay and connecting the ducts to the underside, was my next option. An HVAC tech is coming today to evaluate my project.

    Thanks again!

  4. #4
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,390

    Default

    The evaporator coil of my air conditioning unit fits inside of my air handler, beneath the fan. Are you sure yours doesn't have space for that there? This would leave the entire area above the air handler for your plenum/distribution box. If the a/c unit is not the same brand as the air handler, you may have to fabricate some brackets to hold the evaporator in place, along with the drain, but it probably will fit.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  5. #5
    Retired prof. engr. gator37's Avatar
    Join Date
    Nov 2009
    Location
    Alabama
    Posts
    108

    Default

    Do you have a return air plenum or is the unit on the floor with a side return duct. If on a plenum you may be able to lower the return plenum height as long as it is of adaquate size for the return giving you enough space for your supppy connection OR can your cased coil (a frame I suspect) AND furnace be placed horizontal (Coil has to be made for it with an alternated condensate drain connection and the furnace has to be made for horizontal installation.)? I would not reduce the duct system especially on a furnace.