I have a small staple up under floor radiant heating system.
Right now 8 zone manifold that I am using 5 zones, will be adding 3 more zones in the near future.
I am running supply temp of 140deg F (it actually runs at 137 / 138deg F)
The return temp is between 126 and 128deg F, so it runs between 8 to 10deg F cooler.
Is this a good ratio?

Thanks for any info.
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
If the zones were too large, the return temperature would be much lower and the "end" of the system would be starved of heat. You seem okay, but even if it were not a "good ratio", what could you do about it now?
 

rrekih

New Member
Messages
46
Reaction score
0
Points
0
Location
Canada
It is not a finished area at the moment so I could in worst case scenario do a reconfigure.
 

Zl700

DIY Senior Member
Messages
257
Reaction score
4
Points
18
Location
Western NY
A tight Delta T on radiant flooring can be a good thing, offering even temps however, tight S & R temps on the boiler depending on piping can lead to reduced efficiencies.
 