    Default Utility sink and washing machine

    Can a utility sink and washer share the same 2" drain?
    Both fixtures are vented.

    The utility sink and washer are on adjacent walls, the washer hose does not drain into the utility sink. The washer hose will drain into a 2" standpipe. I was hoping I could tie into the utility drain after the washer p trap.

    (I can post pics if need be)
    Thanks,
    DK

  2. #2
    Master Plumber-Gas Fitter shacko's Avatar
    Join Date
    Jan 2006
    Location
    Rosedale, Md
    Posts
    561

    Default

    If you do what you propose you will end up with a line thats not vented, if both lines are vented a 2in. line is fine.

  3. #3
    DIY Junior Member n2learning's Avatar
    Join Date
    Mar 2009
    Location
    Missouri
    Posts
    21

    Default

    This is in a basement. Utility sink wtih vent.


    Picture showing the stand up pipe and the vent. Obviously nothing is glued yet....and the vent will be extended of course.


    The drain will then connect to the main drain. Am I good to go with the washer once all fittings are cemented?

  4. #4
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,140

    Default

    Not quite.

    Think about how gravity works here- the trap has to be ABOVE the horizontal drain from the sink.
    Also, a sani-tee is not approved for use on a horizontal line. Some areas will accept it for the vent, but not the drain. Use a wye and 1/8th bend combination instead.

    I would prefer to have the washer standpipe and trap flat against the wall. Check out Terry's picture for an example-

    Last edited by cacher_chick; 03-23-2010 at 07:07 PM.

  5. #5

    Default

    You'll want to install the vent and p-trap on a seperate branch. So, in this case, the vent willl be in the same wall as the p-trap.

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,615

    Default

    The pictures I see do NOT show any vents, or at least none where they should be.

  7. #7
    DIY Junior Member n2learning's Avatar
    Join Date
    Mar 2009
    Location
    Missouri
    Posts
    21

    Default

    How about this? I don't have the vent line in but you can see where it would go. This is just a prototype, I'll probably tighten it up.


  8. #8
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,140

    Default

    Sani-tee transitions horizontal to vertical
    Wye and 1/8 bend transitions vertical to horizontal
    Lose the extra length between the wye and 1/8 bend too.
    Attached Images Attached Images  

  9. #9
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,615

    Default

    You are doing it the hard way. Install a combination Y-1/8 bend next to where the trap will be. Glue a street 2x1 1/2 x 1 1/2 sanitary tee into that, and the trap into the side of the tee. The vents only have to be 1 1/2".

  10. #10
    DIY Junior Member n2learning's Avatar
    Join Date
    Mar 2009
    Location
    Missouri
    Posts
    21

    Default

    Thanks for the illustration, it helps. I had to do an image search for 'wye and 1/8 bend'; that's a fitting I haven't bought.
    Is it okay if the vent is 2" or should it really be 1 1/2"?

  11. #11
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,615

    Default

    It does NOT have to be 1 1/2", but it can be. There is no problem with making vents larger than necessary, it just costs more.

  12. #12
    DIY Junior Member n2learning's Avatar
    Join Date
    Mar 2009
    Location
    Missouri
    Posts
    21

    Default

    How about this?
    (The 2X4 will be gone once I strap the pipes in place.)

    Also, is there a minimum or maximum height requirement for the stand-pipe?