My cycle stop valve is a tank at 50-85 psi and a pressure reducing valve at the house. This gives me big water for roof sprinklers for wildfire which has saved the house once already. I do think about the csv for some rentals and vacation homes I have, but would like to see some side by side comps on KW use from standard to CSV at the same household.
Then the pressure reducing valve is giving you constant pressure at the house, while your pump is cycling itself to death between 50 and 85 PSI. This is also wearing out the bladder in your tank. Not only from the constant cycling, which will burst a bladder like bending a wire back and forth multiple times but, also from the wide bandwidth of 50/85, which will overstretch your bladder ever time the pump cycles on and off.
If it has already saved your house one time, then the most important thing would be to make sure the pump and tank are still in good shape, the next time you have a fire. Letting the pump cycle on and off now, means it may be broke when you really need it later. Over-stretching and cycling the bladder tank multiple times, will burst the bladder, which will also help destroy the pump. Then you will be standing there watching your house burn, because the pump quit when it was needed most, which is when they always quit, and no water is coming out of the hose.
As for the energy use, there have been several "studies" published. Amtrol, who makes pressure tanks, produced the most one sided study available, to try and prove that big pressure tanks are superior to a CSV. Their study, as obviously one sided as it was, could only show .5 Kilowatt per day more energy used with the CSV. So if you pay 10 cents per kw, that would be an extra nickel per day, which adds up to a whopping $18.25 per year. That was just for inside the house use only. If you have irrigation or a heat pump that can cause your pump to cycle excessively, then a CSV will actually decrease the energy consumption. But even if you do not have irrigation or a heat pump and you actually use 18 bucks a year more energy with the CSV, that is very cheap insurance to make your pump and tank last three times longer than usual. Not to mention how much it would be worth to have a pump system that has not been cycling itself to death, and is already on it's last leg, when you have a fire and really need it.
Lastly, the way you are using the pressure reducing valve, your house always has the lowest pressure available from your pump. 50/85 pressure switch, with the PRV set at 50 PSI, means you only have 50 PSI to the house. Using a CSV instead, which is placed before the pressure tank, could deliver a constant 80 PSI to the house, eliminate the cycling you are seeing now, make the pump and tank last longer, which saves you a lot of money, and makes sure the pump isn't completely worn out on the day you have a fire.