    Default Drain & Vent for Toilet

    I wanted to attach an image to show what issue I have. The only way I could figure out how to do it is to start a new post. I appreciate all that commented on my drawing on my previous post and I realize now that it would not work because a portion of the vent would be horizontal below the floor. The issue is, the wall of the bathroom is over the joist and as the image shows, the vent was installed into the room and 45s were used to get the vent to the center of the wall. One of the 45s is visible inside the room next to the wall. Is there a way to do this so the vent does not have to go into the room?


    Name:  IMG_0066 (2)..jpg
Views: 317
Size:  92.7 KB

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default

    Only if the tee can be lowered. Then a street 45 into the bushing and trimming the top of the joist will get it into the wall.

  3. #3
    DIY Junior Member echomitch's Avatar
    Join Date
    Jan 2010
    Location
    California
    Posts
    7

    Default

    Thanks HJ for your help.

  4. #4
    DIY Senior Member DavidTu's Avatar
    Join Date
    Dec 2009
    Location
    Seattle, WA
    Posts
    229

    Default

    I believe you can get a Low-heel 90 that is 3x2 and which may save some altitude; it looks to me like you are using a regular 3" combo there--I am suggesting swapping that out for a 3x2 low-heel 90. From there you can go directly into the 45s rather than first adapting down to 2". Also, can you not use a vent-90 instead of the 45s? That would also save altitude.

    Careful notching the top of the joist though, you cannot notch the middle 1/3 of the joist, if I remember correctly.

  5. #5
    DIY Senior Member dlarrivee's Avatar
    Join Date
    Jun 2009
    Location
    Canada
    Posts
    1,172

    Default

    Quote Originally Posted by DavidTu View Post
    Careful notching the top of the joist though, you cannot notch the middle 1/3 of the joist, if I remember correctly.
    Uhh, its the top and bottom of the joist that you should not be notching.... Why do you think TJIs can have osb between the top and bottom chords?

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default

    I HAVE notched the tops of joists countless times to allow pipes to offset over them, although to be specific, it is more like the edge is trimmed on an angle to give clearance for the pipe.