    I am the President of a 53 unit condo building that is getting quotes on installing a tank less system. The building is leaning towards a Navien system because it is the cheapest. Of course the Navien rep says it is the best on the market but the majority of the other plumbers we have talked to say that parts for the Navien unit are hard to get and could result in down time. Is this true?

  2. #2
    DIY Senior Member zl700's Avatar
    Join Date
    Aug 2009
    Location
    Texas
    Posts
    235

    Default

    Not that they are hard to get just that no one stocks them.
    Same holds true in most tankless for alot of areas.

    People stock heating parts but not tankless parts, I dont get it.

  3. #3
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,714

    Default

    Just curious, but is this going to be 53 Navien units, one per condo, or a lesser number, each to service multiple units or... ???

    Loading 53 x 199KBTU/hr burners to the gas grid within the building could have many unintended consequences and may require some SERIOUS upgrading to the gas distribution plumbing to make it work reliably.