Results 1 to 12 of 12
Thread: Do I need conduit?
    DIY Junior Member
    Dec 2009
    S.E. Kansas
    Default Do I need conduit?
    I could not get any 4-2 wg to connect my air handler to my breaker box so I bought 4 copper and 8 copper single strand. Can I bundle these together and run them through the attic like romex or do they have to run in conduit?
    Electrical Contractor Jim Port's Avatar
    Aug 2009
    Maryland
    Individual conductors like you bought need to be installed in a complete conduit system from the panel to the unit or junction box. You just cannot run conduit part way and slide the conductors through.
    DIY Junior Member
    Dec 2009
    S.E. Kansas
    According to my calculations two 4's and an 8 can run in 3/4" conduit and be within the 40% fill rule. Am I right?
    Aug 2009
    Maryland
    What type of conduit?
    DIY Junior Member
    Dec 2009
    S.E. Kansas
    PVC plastic conduit
    My book says 1".
    DIY Junior Member
    Dec 2009
    S.E. Kansas
    There are two 4's and an 8. I looked at a chart and it said 1" for three 4's, so I calculated it for two 4's and an 8 and got 3/4". Was your chart for two 4's and an 8, or three 4's?
    Aug 2009
    Maryland
    Table C9 only allows 1 #4 in a 3/4, and 3 #4s in a 1", based on THHN
    #4 wire for an air handler?
    Must be heat strips.
    Just get the right cable.
    DIY Junior Member
    Dec 2009
    S.E. Kansas
    You're right. Heat strips it is. I have decided to run them in a 3/4" smurf pipe and see what the inspector says
    Engineer Furd's Avatar
    Jul 2007
    Wet side of Washington State
    I guess that's okay as long as you don't mind doing it over. One-inch conduit is the correct size.
    Aug 2009
    Maryland
    But those red tags add a splash of color.