    Been doing some reading and want to make sure I understand-

    If there are from 7 to 9 current carrying conductors in a raceway, the maximum allowed current is 70% of the rating for the conductor.

    For example, I installed 4- 120v branch circuits (8 conductors) which left the panel in one conduit before splitting off in different directions.

    12 GA THHN/THWN is rated at 25A, & 70% is 17.5A, meaning each branch must be connected to a 15A breaker.

    I found this to be surprising as I had assumed that a larger conduit would circumvent the need for derating.

    Am I applying this correctly?

  2. #2
    Code Enforcement codeone's Avatar
    Join Date
    Sep 2008
    Location
    North Carolina
    Posts
    160

    Default

    You use the 90 degree column from table 310.16 for your derating. #12 is good for 30 amp in the 90 degree column.
    So it would be 30 x 70% = 21Amp you can use a 20 a breaker.
    A larger conduit does not circumvent the need for derating.
    Last edited by codeone; 02-21-2010 at 06:17 PM.

  3. #3
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,146

    Default

    Thanks for that codeone....

    Given the above info, what if my new branch connects to old work that is wired with type TW wire?
    Does the whole circuit have to then be derated in the 60 degree column?
    What if this old work is only 2 conductors in a conduit?

  4. #4
    Code Enforcement codeone's Avatar
    Join Date
    Sep 2008
    Location
    North Carolina
    Posts
    160

    Default

    TW is rated for 25 A in the 60 degree column. #12 is limited elsewhere in the code to 20 A. You would only have a problem if you had TW running in the pipe with the THHN/THWN conductors due to the fact the TW would have to be derated from the 60 degree colum. The TW insulation cannot handle the heat the THHN/THWN insulation can. Now if you attach the the THHN/THWN to a TW (to extend the circuit) thats not in the same pipe there would be no problem with the installation.
    If they are in the same pipe you would need to derate for the weakest conductor insulation.

  5. #5
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,146

    Default

    Thank you codeone for taking the time to clarify this for me, I really do appreciate it!