    hi everyone. Please do tell the maximum total degrees of bend permissible before a drain joins the main stack under IPC? I couldnt do a search that wanted to work. Thanks
    not a licensed plumber

  2. #2
    Nuclear Engineer nukeman's Avatar
    Join Date
    Nov 2009
    Location
    VA
    Posts
    696

    Default

    135* before the vent

  3. #3
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,679

    Default

    Your question is ambiguous. It is usually 135 degrees before the vent, but after the vent there is no limitation other than there be cleanouts whenever the line turns more than a total of 90 degrees.