Bimmer
Forget all this hog wash about bonding the pipes in your home. Read the Panel statement from the proposal above and you will see that those charged with writing the NEC seems to think all this bonding around this and that is nothing more than hog wash also.
The only place that bonding of a water pipe is important is if you have 10 feet or more in contact with earth which would make it a grounding electrode. I have already covered what the purpose of an electrode is so I won’t rehash that.
In order for current to flow there must be a complete path from the source back to the source just as in any flashlight. Current leaves the battery goes through the conductor of the flashlight through the bulb back to the battery.
If you were feeling a shock from the water there would have had to been a complete path from the transformer supplying your home back to the transformer.
If the metal box was properly bonded to the equipment grounding conductor then any and all current would have had a path back to the source which would have opened the overcurrent device.
If the box was not properly bonded and there was a problem with the light fixture then it is possible that current was entering the water pipe through the box and through your body down to the concrete back on the grounding electrode conductor and completing the path to the source. When you removed the fixture and box you cleared the fault.
When reinstalling the fixture check that the equipment grounding is connected to any and all metal and check the fixture for any failure. Corrosion of the interior of the light could be your problem