Originally Posted by
drick
Lets go back a second to all the piping being copper. Lets say there is a high resistance short inside the box. Its a high resistance short so the breaker doesn't trip but there is power flowing from hot to ground. Ok, now you cut out part of the copper pipe and replace it with pex effectively defeating the bonding of the copper pipe at the panel. Now when you use the water you get a shock. You discover that the box is touching the copper pipe, you move it and then no more shocks.
One or more of the following is therefore true. 1) The box is not grounded. If it was you would have still had a path back to the panel so you would have not been shocked. 2)The ground wire has a break in it or is not connected someplace so essentially the box is not grounded. 3) When measuring the voltage between the white wire (neutral) and the ground wire the voltage is not 0. 4 When measuring voltage between hot and neutral and then hot and ground you get different readings. They should be around 120V, but its more important that the readings are the same.
-rick