I have a house in a neighbourhood with very high water pressure 100+psi.
A pressure reducing valve was installed and appears to work once there is water flowing,
this was tested at various settings and looking at the gauge.

However when there is no water used in the house/flowing, the pressure rises to the 100+psi.
Are PRV valves supposed to work like this or is there a problem with this valve ?

Thanks,

L
 

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
The PRV limits pressure coming into the house. If the pressure is building from the water heater, the PRV is not at fault. Do you have a working expansion tank?
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
WIth a PRV, you need a working expansion tank so the WH operation which causes the water to expand when it works, has someplace to go. If that isn't the reason for the pressure rising, then the PRV is defective and needs to be replaced or rebuilt. It could be letting pressure rise because of a bad internal seal, dirt, or other defect.
 

lennyk

New Member
Messages
16
Reaction score
0
Points
1
Location
Port-of-Spain
yes, there is no expansion tank, should I just have one installed nearest to the cold input of the water heater ?
Also are expansion tanks the same as water pump pressure tanks ?
 

lennyk

New Member
Messages
16
Reaction score
0
Points
1
Location
Port-of-Spain
I ran some tests tonight with a pressure gauge, both with the water heater on and off.
The heater is not the problem as the pressure creeped up to max on the gauge.
Good thing is that the mains is split into two -
one for a tank supply which feeds a pump in case water mains supply is off
and secondly into the house via the PRV.
I removed the PRV and shut off that supply, I think I am going to leave it that way and have one less
thing to go bad and just run the house off the pump supply and let the float valves in the tanks take the high pressure instead.
 