(206) 949-5683, Top Rated Plumber, Seattle
Results 1 to 9 of 9

Thread: Tie sink vent & boiler vent together?

Hybrid View

  1. #1
    DIY Junior Member zaothusia's Avatar
    Join Date
    Oct 2008
    Location
    Minneapolis MN
    Posts
    5

    Exclamation Tie sink vent & boiler vent together?

    I have a wall mounted high efficiency boiler. It is direct vented with 3 inch PVC outside the house. I am going to be adding a sink and need to vent it quickly, can I tie into this, or will it cause my boiler to run less efficient?

    If I cannot tie into this I am wonder if anyone knows if an AAV is legal in Minneapolis, Minnesota? I would prefer to not have to redo this in the future

  2. #2
    Plumber krow's Avatar
    Join Date
    Feb 2008
    Location
    Ontario, Canada
    Posts
    906

    Default

    Quote Originally Posted by zaothusia View Post
    I have a wall mounted high efficiency boiler. It is direct vented with 3 inch PVC outside the house. I am going to be adding a sink and need to vent it quickly, can I tie into this, or will it cause my boiler to run less efficient?
    Don't you dare try that. You could end up killing yourself if any methane gas gets in the boiler while its firing, if you don't blow up the neighbourhood first

    I'm not sure if AVV's are legal in Minneapolis, but it would be better than the original idea.

  3. #3
    Journeyman & Gas Fitter Doherty Plumbing's Avatar
    Join Date
    Jun 2009
    Location
    Penticton, BC
    Posts
    810

    Default

    Quote Originally Posted by zaothusia View Post
    i have a wall mounted high efficiency boiler. It is direct vented with 3 inch pvc outside the house. I am going to be adding a sink and need to vent it quickly, can i tie into this, or will it cause my boiler to run less efficient?
    no..................

  4. #4
    Previous member
    Join Date
    Jul 2009
    Location
    North of the Mason dixon Line
    Posts
    1,150

    Default

    Got to be the best post of the year

  5. #5
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default vents

    That would not be the best idea you have had this year, nor the smartest one. I can just imagine someone doing that, and then using AAV's on all the other drains and wondering why NOTHING drains properly while the boiler is operating.

  6. #6
    DIY Junior Member Daltex's Avatar
    Join Date
    Jan 2008
    Location
    Texas
    Posts
    15

    Default

    I know you wouldn't have posted this if you understood the implications of doing it. Quick answer is for a quick vent use an AAV if only for the one sink. May not be code so you might want to check it out with the city first. They are not quiet btw.

    Problems with connecting the vent to the boiler vent=

    When the boiler fires, it will have positive pressure running in the vent. This could/would cause the exhaust along with the CO and combustion by products to push its way through the sink's p-trap and cause deadly gas to be released inside your home.

    The vent from the sink will be connected to the main sewer line which has methane gas and odors. When the blower is in between cycles, the methane could be vented back inside your boiler. When ignition occurs- bang! There is no p-trap on the exhaust vent so it could also fill the room with methane along with the sewer odor.
    Last edited by Daltex; 01-05-2010 at 02:04 PM.

  7. #7
    Journeyman & Gas Fitter Doherty Plumbing's Avatar
    Join Date
    Jun 2009
    Location
    Penticton, BC
    Posts
    810

    Default

    Quote Originally Posted by Daltex View Post
    When the boiler fires, it will have positive pressure running in the vent. This could/would cause the exhaust along with the CO and combustion by products to push its way through the sink's p-trap and cause deadly gas to be released inside your home.
    What deadly gases? A properly burning gas appliance doesn't produce any deadly gases. You could obviously produce carbon monoxide but it's not a regular byproduct of combustion in anything close to deadly amounts. But don't get me wrong I'm certainly not trying to say this guy should hook up his plumbing vent to his gas vent.


    Quote Originally Posted by Daltex View Post
    The vent from the sink will be connected to the main sewer line which has methane gas and odors. When the blower is in between cycles, the methane could be vented back inside your boiler. When ignition occurs- bang! There is no p-trap on the exhaust vent so it could also fill the room with methane along with the sewer odor.
    You know that natural gas and propane (the stuff being burned in the boilers) are just forms of hydrocarbons so is methane (in fact NG is basically methane).

    Not only that all boilers that are electronically ignited have a prepurge time of the fan to clear the combustion chamber of any gases.

    And on top of that you need the proper mixture of air to methane to combust it. So is it possible that you could ignite methane from the sewer inside the combustion chamber and have it explode all the way back into the city sewer..... absolutely not.

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •