Thread: #10/3 for single wall oven?

  1. #1
    DIY Member Artie's Avatar
    Join Date
    Nov 2009
    Location
    Jacksonville, Fl
    Posts
    46

    Default #10/3 for single wall oven?

    I just want to make sure before I do this. This is a low-line Kenmore singe wall oven. Spec plate in door says: 120/240 3.4Kw. Installation guide calls for a 30-amp breaker. 10/3 is rated for 30 amps. Approximately a 20' run.

    Does this sound ok, or should I go for #8/3 or #6/3?

    Btw, thats 10/3 w/grnd.

  2. #2
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    10/3 is fine.
    Most single wall ovens are a 120/240v-30A circuit.
    Answers based on the 2008 & 2011 NEC. If you're on the '14 already I feel sorry for you.

  3. #3
    DIY Member Artie's Avatar
    Join Date
    Nov 2009
    Location
    Jacksonville, Fl
    Posts
    46

    Default

    Thanks Pete. Now I know why they call you "speedy".

  4. #4
    DIY Member Artie's Avatar
    Join Date
    Nov 2009
    Location
    Jacksonville, Fl
    Posts
    46

    Default

    At the last minute, I decided to upgrade to 8/3 w/gnd. There will be about 12' that will run through the attic, (going across a now-enclosed carport roof), here in a Florida home. NEC 310.15 (A)(2) says something about reduced ampacity if a high-temp section exceeds 10 ft.