10/3 is fine.
Most single wall ovens are a 120/240v-30A circuit.
|
|
|
I just want to make sure before I do this. This is a low-line Kenmore singe wall oven. Spec plate in door says: 120/240 3.4Kw. Installation guide calls for a 30-amp breaker. 10/3 is rated for 30 amps. Approximately a 20' run.
Does this sound ok, or should I go for #8/3 or #6/3?
Btw, thats 10/3 w/grnd.
10/3 is fine.
Most single wall ovens are a 120/240v-30A circuit.
Thanks Pete. Now I know why they call you "speedy".![]()
At the last minute, I decided to upgrade to 8/3 w/gnd. There will be about 12' that will run through the attic, (going across a now-enclosed carport roof), here in a Florida home. NEC 310.15 (A)(2) says something about reduced ampacity if a high-temp section exceeds 10 ft.