    I thought it looked low too.
    That was a picture sent to me by someone that was installing vessel sinks.

    She is having drain problems related to the small grid drains.

    Yeah, must be a tiny daycare bathroom.

    I believe she said the work had been done by a "Handyman".

    More drywall should have been cut, and the revent 6" higher then the vessel sinks.

  2. #17
    Plumber Winslow's Avatar
    Join Date
    Dec 2005
    Location
    Hawaii
    Posts
    450

    Default

    Quote Originally Posted by Terry View Post
    I thought it looked low too.
    That was a picture sent to me by someone that was installing vessel sinks.

    She is having drain problems related to the small grid drains.

    Yeah, must be a tiny daycare bathroom.

    I believe she said the work had been done by a "Handyman".

    More drywall should have been cut, and the revent 6" higher then the vessel sinks.
    The way some of them grid drains are constructed the sinks won't drain properly, they drain slowly then when enough head pressure builds up it dumps. Not sure if maybe the openings in the grid don't equal the cross section of the drain as required, but Ive run into that problem before.

    Regarding the the picture if the furthest sink was within 3 1/2 feet I would stack the tee's and wet vent the lower drain.
    Last edited by Winslow; 01-15-2010 at 09:18 PM.

  3. #18
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,195
    Blog Entries
    1

    Default

    One more way.


  4. #19
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,624

    Default

    quote; Double vanity at a child daycare?

    Codes do NOT make exceptions for a daycare center. What happens when it becomes an "adult facility" and the sinks are raised? That is why the code says, "42" or 6" above the sink rim, whichever is HIGHER", they are considering what COULD happen down the road, NOT what is happening now. The problem with grid stainers is that the openings are not large enough to allow the air to escape while the water is trying to flow into them. Inserting a straw into a hole or making the holes larger will permit full drain flow. The same thing happens with "rainfall" shower heads which are installed perfectly flat/horizontal. There are a lot of ways to do the drainage, depending on how much time and money he wants to use.
    Last edited by hj; 10-16-2010 at 04:55 PM.

Similar Threads

  1. Single to Double Sink Vanity (again)
    By SAS in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 30
    Last Post: 07-11-2011, 02:31 PM
  2. another Single Vanity to Double Vanity thread, IPC
    By tekmassa in forum IPC Plumbing Code Questions
    Replies: 12
    Last Post: 06-05-2010, 01:30 PM
  3. Yet another single to double vanity post
    By xr4ti in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 11
    Last Post: 04-12-2009, 07:48 AM
  4. Converting single vanity into double
    By rhosch in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 12-31-2008, 05:38 PM
  5. Double vanity from single
    By nc8861 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 07-31-2008, 07:21 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •