    Default Vertical Drain Drop Limit?

    I have a shower on the first floor and I am going to remodel my laundry room in the basement into a bathroom/laundry room. The shower on the first floor isn't properly vented so I am wondering if I can include it in the basement remodel since I can access it from underneath.

    I was wondering if there is a maximum distance from the lip of the floor drain in the shower to the trap wier or another part of the trap?

    The lower I can put the trap the better since I plan to run a vent (within the critial distance) as I am showing in the attached drawing. The vent will be tied into the shower drain and both will run along a wall where the drain will drop and meet with the drain for the washing maching. The vent for the washing machine will go up along the wall and both will combine above the shower trap and connect to one of our stacks in the attic.

    Is there a maximum length for a 1.5" or 2" vent?

    Thanks for the help
    Attached Images Attached Images

  2. #2
    Journeyman & Gas Fitter Doherty Plumbing's Avatar
    Join Date
    Jun 2009
    Location
    Penticton, BC
    Posts
    810

    Default

    Quote Originally Posted by bengal21 View Post
    I have a shower on the first floor and I am going to remodel my laundry room in the basement into a bathroom/laundry room. The shower on the first floor isn't properly vented so I am wondering if I can include it in the basement remodel since I can access it from underneath.

    I was wondering if there is a maximum distance from the lip of the floor drain in the shower to the trap wier or another part of the trap?

    The lower I can put the trap the better since I plan to run a vent (within the critial distance) as I am showing in the attached drawing. The vent will be tied into the shower drain and both will run along a wall where the drain will drop and meet with the drain for the washing maching. The vent for the washing machine will go up along the wall and both will combine above the shower trap and connect to one of our stacks in the attic.

    Is there a maximum length for a 1.5" or 2" vent?

    Thanks for the help
    In Canada here you are allowed upto 1200mm (or 4') on your fixture outlet pipe... not sure about your local codes though.

    The max length for a vent depends on how many fixture units it's venting etc... but the max is usually farther then you'd ever run in a house. For example you can run 30m (~100') on a 1.5" vent that is venting 8 fixture units. The same 2" vent could run 61m.
    Last edited by Doherty Plumbing; 12-29-2009 at 04:23 PM.

  3. #3
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,201
    Blog Entries
    1

    Default

    UPC Code says nothing over 24"

    The vertical distance between a fixture outlet and the trap weir shall be as short as practicable, but in no case shall the tailpiece from any fixture exceed 24" in length.

  4. #4
    Journeyman & Gas Fitter Doherty Plumbing's Avatar
    Join Date
    Jun 2009
    Location
    Penticton, BC
    Posts
    810

    Default

    (deleted) Just checked my code book and in the appendix there is an arrow going to the tail piece calling it the fixture outlet pipe!
    Last edited by Doherty Plumbing; 12-29-2009 at 05:43 PM.

  5. #5
    DIY Junior Member bengal21's Avatar
    Join Date
    Dec 2009
    Location
    Des Moines
    Posts
    21

    Default

    Thanks to you both.

    Looking at my drawing a second time I show that the vent would go "to roof" but I plan to tie into one of the other stacks in the house. is what I show acceptable under UPC? Could I slope the vent line for the shower 1/4" per foot either direction since either direction will allow it to drain?

  6. #6
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,201
    Blog Entries
    1

    Default

    The vent for the washer downstairs and the vent for the shower can revent above the flood level of the highest fixture in that group.
    If there is a lav connected, it would be six inches above the counter height.
    The revent would be on the floor of the shower.
    Not below the floor.

    You can run vents pretty flat when above the flood level,
    Below that, and it needs grade.

    Last edited by Terry; 12-29-2009 at 07:09 PM.

  7. #7
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,146

    Default

    What you have drawn definitely won't do. The shower vent cannot run horizontal until it is above the flood rim of the highest fixture on the vent.