What is standard size PEX ?

Users who are viewing this thread

Mudball

New Member
Messages
84
Reaction score
0
Points
0
Location
TN
For running supply lines to bathrooms and kitchen ? We dont have anything extra out of the ordinary. Bathroom is tub/shower, toilet, and sink. The kitchen will have sink and possible future dishwasher. So then would the 1/2" PEX supply lines be alright or would we need to consider larger ?
 
Last edited by a moderator:

JohnjH2o1

Plumbing Contractor for 49 years
Messages
1,188
Reaction score
13
Points
38
Location
Florida
Run 3/4' mains with 1/2" branches to each fixture. Avoid putting two fixtures on 1/2".

John
 

Mudball

New Member
Messages
84
Reaction score
0
Points
0
Location
TN
I think I understand. I want to make sure the plumber runs 3/4" hot/cold supply lines to the bathrooms but branches off from that 3/4 and go down to 1/2" for each individual fixture. Each bathroom will have toilet, sink, and shower so I guess 1/2" wont be enough to be a supply line for those three.
Thanks for the help
 