    Default Mystery Boiler from hell

    After all sorts of trouble...it was working, circulating...every radiator heating....I was convinced that it had been a lack of water and pressure, it ran great for hours...then we woke up cold. The aquastat askes the pump to circulate at the call for heat...whether or not the blower and burners are on..was working last night for the first time in 5 weeks....now it is back to the 3 or 5 minutes to heat up and shuts down....I rebled the all the radiators, but still only 3 to 5 minutes and it shuts down cuz it is to limit..

    It has to be the pump..????

    Ideas?

    cristan

  2. #2
    Previous member
    Join Date
    Jul 2009
    Location
    North of the Mason dixon Line
    Posts
    1,150

    Default

    have you tested the pump yet?

    why not call a heating tech and get it over with?

  3. #3

    Default

    Is it a lack of water in the tank itself? I am no expert so get your "grain of salt" out. It would seem to me that you could heat a small amount of water and a lot of air to the stop temp in 4 to 5 minutes, but not a large amount of water. I would try adding water to the tank, opening the release, see if air comes out, then adding more. If it is still circulation, what pump would be broke? The fuel pump? if so $5.95 for a gage and couple bucks more for the male/male threaded 3/8 connect.

    Please remember I am crazy.

  4. #4
    DIY Junior Member mudslider's Avatar
    Join Date
    Dec 2009
    Location
    wa
    Posts
    21

    Default tried a tech

    This all started with a tech coming out and saying he didn't know what was wrong, everything tested ok...not sure how to run the pump pulled....it is a taco007 with a cart. Guess I get to pay again....it has beat me. Grandkids coming to a cold house.

  5. #5
    DIY Junior Member CtSebby's Avatar
    Join Date
    Dec 2009
    Location
    ct
    Posts
    14

    Default

    You don't have to un-plum the circulator just unwire it from the aquastat and hook it to straight 110 volts to see if it runs.

  6. #6
    DIY Junior Member mudslider's Avatar
    Join Date
    Dec 2009
    Location
    wa
    Posts
    21

    Talking Finally

    Well, I think we had two issues...Low water and air AND an intermediate short in the wiring at the pump. My step son as here for Christmas, he is a journeybman Electrician. We thought it was the pump and he confirmed and was able to "fix" it until we can replace it.
    Thanks for all the input..it all helped.

    Cristan