    Default furnace-no ignition

    I have a Lennox G26Q3-75-1 that will not ignite. With a call for heat, the combustion blower runs contiuously and that's it. The igniter does not come on and I suspect that the gas valve is not opening. The blower motor operates on the fan only mode from the thermostat. The honeywell ignition system update has been installed already. Any ideas?

    Thanks

  2. #2
    Senior Robin Hood Guy Ian Gills's Avatar
    Join Date
    Jul 2007
    Location
    USA
    Posts
    2,781

    Default

    The transformer may have gone or a fuse on the board might have blown.

    Make sure you disconnect the power before you go in there.
    Last edited by Ian Gills; 12-20-2009 at 05:22 PM.

  3. #3
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,395

    Default

    Closed combustion burners have a pressure switch that ensures the air supply and vent are working properly. There's usually a vacuum hose going to the switch. If it has cracked or come loose, the switch won't open, and the burner won't fire. There are other reasons why it might not work - blocked vents or flue, or cracks. The diagram on the device will often have a schematic of the safety interlocks. You can usually figure out where the interlock is open, and isolate it to the appropriate control. If it actually tries to fire and doesn't detect flame, the flame sensor may be dirty or shot. Sometimes, there's a flashing light on the control board that tells you something if you have the manual.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  4. #4
    DIY Junior Member pitteach's Avatar
    Join Date
    Jan 2008
    Location
    Hamburg, NY
    Posts
    27

    Default

    It was the pressure switch. All is well. Thanks for the responses.