    I have read a couple of threads I found through the search function and am still not clear on the requirements. Any clarification would be appreciated.

    I propose to install a couple of recessed light cans directly in the shower, in addition to a vent fan. The clarification I am looking for is:

    1. Do I understand correctly that the recessed cans can be run on the same lighting circuit as the recessed cans in the main part of the bathroom? This is a small bathroom with 4 cans total, 2 main, 2 shower. That circuit will most likely also run two sconces R&L of the mirror.

    Is this ok or do I need to gfci the recessed cans over the shower.

    2. Am I correct in understanding that the fixture needs a “damp rating” combined with the shower trim to be appropriate, or do I just need a shower trim?

    3. I am planning a separate 20 amp circuit to the fan. Run from panel to gfci receptacle, then timer switch, then fan. Is this correct.

    Thanks in advance for any help

    Jim

  2. #2
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    976

    Default

    The lights can be on the same lighting circuit as the room. No GFI protection is required unless the mfg requires it. VERY few do.

    Almost all recessed housings (cans) and trims are damp rated. You only need a wet location shower trim if the light is subject to shower spray. Most simply install these trims regardless.

    WHY would you run a dedicated 20A circuit to a bath fan???? Does it have a heater? If so then I bet the instructions call for not installing it over a tub or shower.
    Also, WHY install it over the shower to begin with? There is NO difference in the venting efficiency if it is in the room outside the shower, especially a small room like you have.
    Is the shower stall sealed off from the room?
    Answers based on the 2008 & 2011 NEC. If you're on the '14 already I feel sorry for you.

  3. #3
    DIY Junior Member
    Join Date
    Dec 2009
    Location
    MA
    Posts
    3

    Default

    Speedy,

    Thanks for the clarification on the cans.

    As for the fan, I was thinking of putting in a soffit to kind of separate the tub from the room a bit. I like the symetry of the recessed cans in the main part of the room and the vent fan kind of throws that off. If I mount it in the shower, I get the benefit of improved aesthetics, and draw the intake air through the damp shower, possibly removing the moisture more quickly.

    There is no heater in the fan.

    The 20 amp gfci is for the plug that will be in the bathroom. MFG spec indicates if the fan will be over the tub/shower it must connected to a gfci protected branch circuit. I wanted to confirm if running off the plug provided that protection.

    The unit I am installing is Fantech PB100 which will actually be mounted in the attic away from the shower. This is causing me the confusion as to gfci it or not.

    Jim
    Last edited by fatalbie; 12-19-2009 at 12:56 PM. Reason: PB100 not _B100

  4. #4
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    976

    Default

    Quote Originally Posted by fatalbie View Post
    The 20 amp gfci is for the plug that will be in the bathroom. MFG spec indicates if the fan will be over the tub/shower it must connected to a gfci protected branch circuit. I wanted to confirm if running off the plug provided that protection.
    I see. Your original post made it seem like the 20A circuit would be just for the fan.
    Your plan sounds fine.
    Answers based on the 2008 & 2011 NEC. If you're on the '14 already I feel sorry for you.

  5. #5
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,428

    Default

    One thing to consider if the fan is in the shower area, the nice hot/humid air it sucks out will be replaced by the much colder room air...you'll be standing in a draft all the time. I don't think you'll like it.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  6. #6
    DIY Junior Member
    Join Date
    Dec 2009
    Location
    MA
    Posts
    3

    Default

    Thanks for the input and the quick response; I appreciate it.

    Nashua- I thought about that. It will be a trade off I have to live with in exchange for the aesthetics. If it is a big negative after the install, I can make the change with some patch work. Unfortunately, the plastering end of it I am way too familiar with.

    Jim

  7. #7
    Jack of all trades frenchie's Avatar
    Join Date
    Dec 2006
    Location
    Brooklyn, NY and Fire Island, NY
    Posts
    1,244

    Default

    If the fan is on a separate switch - and it sounds like it will - you can just not run it during your shower, turn it on when you get out. S'what I do.
    Master Plumber Mark:

    there is nothing better than the
    manly smell of WD 40 in the air
    while banging away on brass with a chisel and hammer...

    it smells like......victory......

    do not hit your thumb...