    Default Acid Neutralizer Installation Questions

    Hello All,

    I recently purchased an acid neutralizer for my house and had a couple questions regarding the installation. A lot of my questions have to do with recent reading - it appears PVC pipe (not CPVC) is NOT allowed IN the house for cold water applications. This has me worried as the previous owner plumbed in a softener with PVC piping (it does say "drinking water" on it)...

    • I have a call in to my local code enforcement office (SE PA - uses IPC 2003), but, in the meanwhile, can anyone confirm that it is/is not against code to use PVC in the aforementioned application?
    • If PVC is against code, is there anything else that's okay to use (other than CPVC, PEX, and Cu)? Flex PE (black)? Others?
    • Any pipe preferred over the others?
    • If PVC is against code, why is the acid neutralizer adapter (to house plumbing) sized with a female 3/4" PVC?
    • Are there special 3/4" CPVC adapters that have the same OD as the 3/4" PVC?
    • If not, how would you all recommended attaching the acid neutralizer to my in house plumbing (probably going to use 3/4" CPVC)
    • I haven't run the numbers, but in real world applications (40-65psi) would there be any noticeable flow loss from the 3/4" CPVC v. PVC? I'm assuming the IDs are different...
    • There is currently a pressure gauge after the water treatment; it looks like there is a 3/4" PVC "saddle" (glued overtop pipe) with 1/4" female NPT that the gauge is screwed in to. Do they make these similar "saddles" for CPVC? Or, am I better off finding a T fitting with the same specs? I didn't see any saddles at McMaster Carr.


    Thanks in advance!

    Best,
    Alex

  2. #2
    That's all folks! Gary Slusser's Avatar
    Join Date
    Aug 2004
    Location
    Wherever I park the motorhome.
    Posts
    6,790

    Default

    PVC is approved for cold water only potable water use. IMO it is the best choice for your type of equipment because it is inexpensive, easy to use, it has a larger ID, it is iron pipe size (IPS maintains the ID) than copper tubing size (CTS maintains the OD) PEX, copper and CPVC.

    If it were mine I'd leave it alone and as long as it was supported where needed (like for spans over 4-5') I wouldn't worry if it was in my basement to my water treatment equipment.
    Gary Slusser Retired (= out of business)
    Click Here to learn how to correctly size or program a water softener.
    CAUTION, as of Nov 12 2013 all YouTube videos showing how to rebuild a Clack valve have an error in them that can cause damage.

  3. #3
    Previous member
    Join Date
    Jul 2009
    Location
    North of the Mason dixon Line
    Posts
    1,150

    Default

    [QUOTE=ACEschborn;239166]Hello All,

    I recently purchased an acid neutralizer for my house and had a couple questions regarding the installation. A lot of my questions have to do with recent reading - it appears PVC pipe (not CPVC) is NOT allowed IN the house for cold water applications. This has me worried as the previous owner plumbed in a softener with PVC piping (it does say "drinking water" on it)...

    • I have a call in to my local code enforcement office (SE PA - uses IPC 2003), but, in the meanwhile, can anyone confirm that it is/is not against code to use PVC in the aforementioned application?

      Neither IPC nor UPC allows the use of PVC for distribution piping within the structure. (table 605.5)

    • If PVC is against code, is there anything else that's okay to use (other than CPVC, PEX, and Cu)? Flex PE (black)? Others?

      The above listed are approved with the exception of PE
    • Any pipe preferred over the others?

      It is a matter of personal preference
    • If PVC is against code, why is the acid neutralizer adapter (to house plumbing) sized with a female 3/4" PVC?

      It isn't. It has a 3/4 ips thread that will adapt to most anything
    • Are there special 3/4" CPVC adapters that have the same OD as the 3/4" PVC?

      Yes
    • If not, how would you all recommended attaching the acid neutralizer to my in house plumbing (probably going to use 3/4" CPVC)

      Get 3/4 threaded coupleings and 3/4" cpvc male adaptors

    • I haven't run the numbers, but in real world applications (40-65psi) would there be any noticeable flow loss from the 3/4" CPVC v. PVC? I'm assuming the IDs are different...

      so minimal as to be of no concern

    • There is currently a pressure gauge after the water treatment; it looks like there is a 3/4" PVC "saddle" (glued overtop pipe) with 1/4" female NPT that the gauge is screwed in to. Do they make these similar "saddles" for CPVC? Or, am I better off finding a T fitting with the same specs? I didn't see any saddles at McMaster Carr.


    That is an illegal hack job, you can get the proper adaptors. Saddle valves are illegal for all uses


    Thanks in advance!

    Best,
    Alex[/QUO


    As always, check with local code authority

  4. #4
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    PVC pipe is not approved for water supply piping, and it based totally on the temperature/pressure ratings curves of PVC. The max pressure drops off significantly above 72. I suppose the theory to ban it completely is that if you allowed it for "cold only", there is too much possibility that there would be mixups/=.

    But the use of PVC is NOT banned for fittings, such as filters or your gizmo, maybe just a loophole, and maybe because they are clearly "cold only" install.

  5. #5
    DIY Junior Member ACEschborn's Avatar
    Join Date
    Nov 2009
    Location
    Pennsylvania
    Posts
    14

    Default

    Well, I remain confused. Through my forum readings, I have come to appreciate both Peter and Gary's posts (sorry Jimbo, don't remember reading your posts), however, they seem to disagree on this topic...

    Gary, can you confirm/provide reference to where PVC is okay for cold, potable water?

    Thanks again!

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,624

    Default Pvc

    What kind of connection is the female PVC? If it is a thread, you NEVER want to screw a metal male thread into it. Even a male PVC/plastic adapter can create enough stress to crack the attachment. PVC has a history of spontaneous failure, usually in the joints but also in the fittings, (I replaced a PVC tee last week which had cracked through the backside of it, but have had it happen to elbows and 45's over the years.).

  7. #7
    DIY Junior Member ACEschborn's Avatar
    Join Date
    Nov 2009
    Location
    Pennsylvania
    Posts
    14

    Default

    Quote Originally Posted by hj View Post
    What kind of connection is the female PVC? If it is a thread, you NEVER want to screw a metal male thread into it. Even a male PVC/plastic adapter can create enough stress to crack the attachment. PVC has a history of spontaneous failure, usually in the joints but also in the fittings, (I replaced a PVC tee last week which had cracked through the backside of it, but have had it happen to elbows and 45's over the years.).
    It is NOT threaded, but rather a female slip/glue fitting. Sorry I don't know the technical term.

  8. #8
    Previous member
    Join Date
    Jul 2009
    Location
    North of the Mason dixon Line
    Posts
    1,150

    Default

    I don't want to dredge up old arguments but I can tell you that none of the nationally used and accepted codes allow PVC to be used within the structure for potable water distribution piping. IPC table 605.4 lists all of the acceptable materials.

  9. #9
    DIY Junior Member ACEschborn's Avatar
    Join Date
    Nov 2009
    Location
    Pennsylvania
    Posts
    14

    Default

    Understandable, Peter, and thank you.

    Any idea why PVC is okay in fittings (such as the 3/4" PVC elbows that came with my acid neutralizer)?

    For the 3/4" PVC female (slip/glue) fitting, I'm thinking about using a CPVC adapter (3/4" PVC OD, with 3/4" CPVC connection). Should the big box stores carry this?

    Thanks again for everyone's help!

    ACE