The exterior "power inlet" as you describe it should be in a weatherproof box and the conduit should connect directly to it.
|
|
|
Hello,
Basic question, but I dont know the correct answer.
I am putting in a transfer switch. I am using 3/4" sch40 conduit from the exterior power inlet to the transfer switch....and pulling in 4 #10 stranded.
My question is how to attach (what fittings, etc) the sch 40 to the exterior power inlet.
The sch40 will go down between the garage doors and the power inlet is on the exterior siding between the garage doors. The wall is approx 6" ( drywall, stud, plywood sheething and siding).
I was told to use a liquid tight fitting up against the box...??
What else?
Thanks,
Homer
The exterior "power inlet" as you describe it should be in a weatherproof box and the conduit should connect directly to it.
http://www.inspectpa.com/forum/forum.php
My answers are based mostly on the ICC codes. Advice given is my personal opinion and every person performing work should acquire a permit from his/her jurisdiction and get the work inspected. My opinions are not directions to follow for DIYs or professionals
Yes, it is an official 30a exterior power inlet by GenTran......
I have been looking online and have comeup with this....
Inlet box -> LiquidTight 3/4 connector -> 3/4 LT NM conduit (just enough to get me in the 6" wall and up about 6" and then transition to sch 40 with a coupling....
Does this sound correct?
Thanks in advance.
Homer
Is there a knock out on the box or do you have to make your own?
All you need is a male fitting with a locknut inside the box.
Is this the power inlet box that has the outlet on the bottom?
http://www.inspectpa.com/forum/forum.php
My answers are based mostly on the ICC codes. Advice given is my personal opinion and every person performing work should acquire a permit from his/her jurisdiction and get the work inspected. My opinions are not directions to follow for DIYs or professionals
Yes, it has a couple of knock outs and the outlet is on the bottom.
AS long as you don't exceed 36- degrees between pull points, you should be fine.
http://www.inspectpa.com/forum/forum.php
My answers are based mostly on the ICC codes. Advice given is my personal opinion and every person performing work should acquire a permit from his/her jurisdiction and get the work inspected. My opinions are not directions to follow for DIYs or professionals
Thanks...
Actually have 450 degrees of bends.....five 90's to be exact...(90 to go up the wall between the garage doors, 90 at the ceiling to go down the center of the garage ,a 90 2/3 the way down the center of the garage to turn it towards the panel, 90 at the ceiling to turn it down the wall and a 90 to turn it into the panel.
I was thinking of putting two pull points.....
Thanks for all your help.
Thats what I heard....
...any other ideas.....
Thanks again
You simply need to add another weatherproof pull point such as an LB that is accessible.
http://www.inspectpa.com/forum/forum.php
My answers are based mostly on the ICC codes. Advice given is my personal opinion and every person performing work should acquire a permit from his/her jurisdiction and get the work inspected. My opinions are not directions to follow for DIYs or professionals
..i was going to put in two access points....
thanks
Also there is "wire pulling lubricant" which makes wire pulling a lot easier.
Like this...
(They would have this at a home improvement store electrical department.)
http://ideal.datacomtools.com/idealc...-lubricant.htm
The code only allows 4 , 90 deg bends before a junction is required, so i would go 3 then a junction and 2 more. The weather proof box does not require liquid tight . thats why the holes are in the bottom and there are tiny drain holes in the corner . I would come out of the bottom with a lock nut and male adapter then short pipe and an LB then thru wall and put silicon where you penetrate the wall . That will get you inside and around the first 90 . Its not the professional way but it helps to slide the pipe and fittings over the wire and glue them as you go instead of installing all the conduit and trying to pull all at once , It takes a lot of experience to determine if a pull is going to be a hard one , That way you dont have to worry. If you are going in attic or places not exposed you can change over 10/4 nm at a junction , thats a lot easier than conduit.
Last edited by jetlag; 12-13-2009 at 05:55 PM. Reason: add more