I have a dumb question. I have a boiler system my question is, once the system is filled and the correct PSI is reached does the gate valve have to be closed or does it need to remain open? The gate valve is before the reducing valve.
 

JohnjH2o1

Plumbing Contractor for 49 years
Messages
1,188
Reaction score
13
Points
38
Location
Florida
The valve should remain open as long as there is a reducing valve between the valve and the boiler.

John
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
The system should also have a check valve to prevent stagnant boiler water from potentially back flowing if there were a hiccup.
 