Results 1 to 15 of 18
Thread: Sub-Panel Neutral and Ground Bonded
Hybrid View
    DIY Senior Member TJanak's Avatar
    Sep 2009
    South TX
    Default Sub-Panel Neutral and Ground Bonded
    The sub panel in my 40 year old house has all of the neutral and grounds on the same bus. I know this is incorrect but would like to figure out the best way to fix it. The current wire feeding the panel from the main is a 2 wire plus ground "romex" type insulated cable. It feeds the whole house other than the A/C compressor so this feed is probably 4-6 gauge (EDIT: actually looked at it today and it's #2) because it makes a 55' run from the main panel. The ground on this cable is non insulated like in a romex type cable.
    To separate the neutrals and grounds I would assume I need to add another bus bar and then run another wire from the main panel to the sub. Would this new wire need to be the neutral since my current ground is non insulated? If so, I assume it would need to be the same gauge as my current hot feed?
    Lastly, how important is it that I fix this? I also need to add GFCI's in bathrooms and the kitchen (maybe a GFCI breaker in the sub panel) and wasn't quite sure if this neutral ground bond issue at the sub panel would affect GFCI operation.
    If it has been like that for 40 years leave it alone unless you are willing to run a new 4 wire cable.
    http://www.inspectpa.com/forum/forum.php
    My answers are based mostly on the ICC codes. Advice given is my personal opinion and every person performing work should acquire a permit from his/her jurisdiction and get the work inspected. My opinions are not directions to follow for DIYs or professionals
    Remodel Contractor GabeS's Avatar
    Jan 2007
    Brooklyn NY
    If the neutrals and ground are joined then you could get current on the ground wires. The ground should not carry current. Do you mean that you have a three wire plus ground coming into the panel? Two wire and ground would only be 110 volts.
    Jar, why do you recommend to leave it alone? Isn't it a potentially dangerous situation?
    Gabe
    Don't follow my advice, I only know a thing or two about a thing or two.
    Extreme DIY Homeowner Scuba_Dave's Avatar
    Jan 2009
    South of Boston, MA
    2 hots+neutral=240v, used to be the way things were run-not sure how long ago
    How many wires from your POCO ? - never seen 4
    Plenty of places still hooked up this way
    DIY Handyman (not 4 hire)
    I have enough to do to my own house
    Quote Originally Posted by GabeS View Post
    If you read what I said again, my intention was to basically say that anything short of running a new 4 wire cable is a waste. If you are not going to do it right then don't do it at all.
    That's the way it was done in the olden days.
    Don't mess with it unles you are doing some major work or replacing the panel.
    Default wire
    HOW olden days was it. That type of cable is often aluminum. Connect the grounds to a new bus bar, and connect THAT to a ground rod. Leave the current third wire as the neutral. BUt as it is now, the grounds are NOT carrying current, unless they are attached to an active circuit at their origination point.
    Sep 2009
    South TX
    Looks to be copper but I'm not 100% sure. Didn't scratch it because it was hot.
    The current third wire comes into the box with no insulation, just like the ground in romex. It touches the sides of the box as it makes its way down to the lug at the bottom. I don't really care for this because of the neutrals and grounds connected to this third wire, specifically the neutrals. It doesn't seem to me to be a suitable neutral due to the lack of correct insulation.
    Also, by the time I get to a suitable location to put in a ground rod I might as well run the extra 10-15 ft. to the main panel. EDIT: frenchie: Don't know why I would do the ground rod though, both main and sub panel are on the house, just opposite sides.
    Dec 2006
    If you want to do it right, it need a ground rod because it's in a separate building, and it needs 4-wire to the main panel.
    Master Plumber Mark:
    do not hit your thumb...
    __________________
    Network Engineer rmelo99's Avatar
    Jul 2006
    Quote Originally Posted by frenchie View Post
    Am I missing somewhere in the post where he said the 2 panels were in sep buildings?
    Code Enforcement codeone's Avatar
    Sep 2008
    North Carolina
    If you take this advice be sure you rewire with a four wire conductor. Otherwise your grounds will be doing nothing. Contrary to popular belief current is not trying to find ground its trying to find its source. You have to have a complete circle. The earth is not a low impediance path for current to follow. Thats why you need the fourth wire. It is true today this situation would not be allowed. However it is permitted to leave the way it is. As long as a dryer or range does not originate out of the sub panel.
    Licensed Electrical Contractor Speedy Petey's Avatar
    Jun 2007
    NY State, USA
    Quote Originally Posted by codeone View Post
    Absolutely agree!
    Simply connecting a ground wire to a ground rod will do absolutely nothing.
    Answers based on the 2008 & 2011 NEC. If you're on the '14 already I feel sorry for you.