Thread: Takagi KD-20 Error Code 21

  1. #1
    DIY Junior Member
    Join Date
    Dec 2009
    Location
    Colorado
    Posts
    2

    Default Takagi KD-20 Error Code 21

    I have a Takagi KD-20 that works for a bit then stops and flashes an error code 21. We haven't had any problems with it before. Today it is -10degrees F with -30 windchill - the only thing that seems different from most days.

    The manual just says "vent pipe".

    any ideas on what is going on here?

    when running inlet temp is 43 and out is at 122 until it stops...so it doesn't appear to be anything freezing.

  2. #2
    DIY Junior Member
    Join Date
    Dec 2009
    Location
    Colorado
    Posts
    2

    Default more info - KD-20 quits working

    To add a little bit to this:
    The furnace and water heater have independent exhaust lines, but common air intake lines (the WH line tee's off of the furnace line).

    The water heater will work fine when the furnace is off, but stops with an error code 21 shortly after the furnace starts.

  3. #3
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,720

    Default

    Presumably it's installed indoors where it's well above 5F, and the backflow preventer is installed on the vent, in which case the electric heat-exchanger heater can and will protect it. The incoming air for combustion can be quite cold and not cause a problem, since the only time it's drafting over the heat exchanger with out the flame is on flue purges, and the air has far less thermal mass than the water in the HX & internal plumbing.

    I too would suspect frost/ice restriction on the air intake under super-cold conditions, especially if the intake is near the exhaust vent to the furnace.

  4. #4
    DIY Senior Member zl700's Avatar
    Join Date
    Aug 2009
    Location
    Texas
    Posts
    235

    Default

    You cant common vent the intake of a heater that has been adapted to 2-pipe.
    The furnace draw is affecting the venting pressure switch of the Takagi.
    Follow the instructions by doing a correct install.

  5. #5
    DIY Junior Member Tecno's Avatar
    Join Date
    Dec 2010
    Location
    maine
    Posts
    2

    Default

    Make sure the backflow preventer is opening all the way..I have a TKJR and it will work with the backflow preventer in the closed position IE it was stuck shut from small particles that had grown on the vent pipe inside.this was causing a pressure Differential some of the time but it must have been very close to the trip point of the Pressure Sensor. I was getting the Pressure switch code 21 I removed the vent and cleaned the inside of the pipe and it fixed the problem..