Thread: Split 110v off a 230v branch circuit?

Hybrid View

  1. #1

    Default Split 110v off a 230v branch circuit?

    Is it possible to split out a 110v branch from a 230v branch circuit? I'd like to put an exterior light and 15A receptacle near my A/C compressor, but it's a 120' run back to the panel, and access it difficult.

    I've got a 230v/50A circuit supplying the A/C compressor and the compressor only requries 35A, so overloading the 50A circuit isn't an issue. The A/C circuit terminates in a fused disconnect box, and then a whip into the unit.

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    19,402

    Default

    Not sure if this is legal, but would only be possible if they ran a neutral. If you only have two wires and ground, then no. If you have three wires plus ground, then yes. From neutral to one hot is 120vac. You'd get the same 120vac from one hot to ground, but that would not be code or safe
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013

  3. #3

    Default

    The 230v circuit is #6-3 w/ground. This will be inspected, so along with safety, code compliance is also important.
    Last edited by jeffeverde; 12-09-2009 at 06:33 AM.

  4. #4
    DIY Member arfeller's Avatar
    Join Date
    Aug 2007
    Location
    Port Angeles, WA
    Posts
    77

    Default

    So, if i understand correctly, you have a 6/3 + ground. So two (2) hots, one (1) neutral, and one (1) ground going to the compressor?

    If you do have the neutral then splitting out a 110 v ciruit should not be a problem. However, you might run into problems with the fused box.

    I had a fused box that would not support splitting a circuit like that so had to replace it with a subpanel. They are pretty cheap ~$35 at home depot + another ~$30 for breakers you might need.

    I recently ran 2x #6 hot, 1x #8 neutral, and 1x #10 ground to a subpanel and have a 220v circuit and two 110 v circuits.

    I'm not an electrician and am only speaking from DIY projects i have recently done.

    So make sure and get comformation of this

  5. #5
    Extreme DIY Homeowner Scuba_Dave's Avatar
    Join Date
    Jan 2009
    Location
    South of Boston, MA
    Posts
    885

    Default

    You want to put a branch circuit on a 50a breaker ?
    DIY Handyman (not 4 hire)
    I have enough to do to my own house

  6. #6

    Default

    Remove your outdoor A/C disconnect and replace it with a small weatheproof subpanel. Add the proper sized 2 pole breaker for the A/C and then add a 20A single pole breaker for your outside outlet. The subpanel will act as a disconnect for the A/C so you will no longer need the disconnect.

    -rick

  7. #7
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    23,717

    Default 230

    VERY few air compressors have a neutral wire, since they do not have any 110/120 volt components. In addition, the circuit breaker is primarily to protect the wires, NOT just the appliance, so any wires connected to that circuit would have to be rated for 50 amps, which is a little large for a duplex receptacle.

  8. #8

    Default

    Quote Originally Posted by arfeller View Post
    Ok, i think there is some confusion about the situation.

    It is my understanding that what Jeff has is:

    120' of 6/3 with ground that runs out to a fused disconnect box. From this box he has wired up the A/C unit. If this is true, there is an unused neutral wire in the circuit that could be used to make the 110v circuit. . . .
    Correct

    Quote Originally Posted by drick View Post
    Remove your outdoor A/C disconnect and replace it with a small weatheproof subpanel. Add the proper sized 2 pole breaker for the A/C and then add a 20A single pole breaker for your outside outlet. The subpanel will act as a disconnect for the A/C so you will no longer need the disconnect.

    -rick
    Thanks for your input, that's what I was thinking.

  9. #9

    Default

    Quote Originally Posted by jeffeverde View Post
    I've got a 230v/50A circuit supplying the A/C compressor and the compressor only requries 35A, so overloading the 50A circuit isn't an issue.
    Ahh,...yes, yes it is an issue.

    What is the motor FLA, FLC, HP & Service Factor
    http://www.inspectpa.com/forum/forum.php
    My answers are based mostly on the ICC codes. Advice given is my personal opinion and every person performing work should acquire a permit from his/her jurisdiction and get the work inspected. My opinions are not directions to follow for DIYs or professionals

  10. #10
    Code Enforcement codeone's Avatar
    Join Date
    Sep 2008
    Location
    North Carolina
    Posts
    160

    Default

    Quote Originally Posted by jeffeverde View Post
    I've got a 230v/50A circuit supplying the A/C compressor and the compressor only requries 35A, so overloading the 50A circuit isn't an issue. The A/C circuit terminates in a fused disconnect box, and then a whip into the unit.
    What is the minimum circuit ampacity for you a/c?
    What is the max breaker size for your a/c?

    These facts are needed to do the calculation you need.

  11. #11
    Code Enforcement codeone's Avatar
    Join Date
    Sep 2008
    Location
    North Carolina
    Posts
    160

    Default

    Quote Originally Posted by jeffeverde View Post
    I've got a 230v/50A circuit supplying the A/C compressor and the compressor only requries 35A, so overloading the 50A circuit isn't an issue. The A/C circuit terminates in a fused disconnect box, and then a whip into the unit.
    The issue is if your minimum circuit ampacity is 35A you haved to multiply 35 x 125% to come up with your calculated load for the circuit. This is for start up current.

    35 x 125% = 43.75 or 44A
    50A - 44A = 6A
    Dont have as much extra as you thought!

    Now if the 35A is you max breaker size you might be ok.
    Give us some more info please.