Thread: bathroom and washroom remodel

  1. #1
    DIY Junior Member
    Join Date
    Dec 2009
    Location
    North Carolina
    Posts
    2

    Default bathroom and washroom remodel

    Hi,
    I'm remodeling our bathroom and moving a washer and dryer to the room behind the bath. I've been reading through the posts, which have been very helpful and have a diagram I would love to get some feedback on. I am using some of the existing plumbing which was done a few years ago. I'm adding the washer, moving the WC and adding a utility sink.

    A friend suggested that I connect the washer below the toilet to avoid bubbles. That is the reason for the parallel 3" line. Is that necessary? Also, do I have enough venting?

    Thanks much for your time and feedback!


  2. #2
    Plumbing Designer FloridaOrange's Avatar
    Join Date
    Dec 2005
    Location
    SW Florida
    Posts
    1,317

    Default

    Are there vents at the lava nd the utility sink? I guess under some conditions you could call what you have a circuit vent but that isn't used too often in residential construction and your vents would be too small for a properly sized circuit.
    Matt
    Semi-professional plumbing designer
    Enjoying life in SW Florida

  3. #3
    Plumbing Contractor for 49 years johnjh2o1's Avatar
    Join Date
    Aug 2009
    Location
    South*East
    Posts
    1,121

    Default

    There must be a vent for each fixture. All you have vented is the main line.

    John

    Helpful Plumbing Hints for Residential Construction by Bert Polk Plumbing Inspector Lincoln County
    Last edited by Terry; 05-24-2010 at 03:25 PM.

  4. #4
    Plumbing Designer FloridaOrange's Avatar
    Join Date
    Dec 2005
    Location
    SW Florida
    Posts
    1,317

    Default

    Quote Originally Posted by johnjh2o1 View Post
    There must be a vent for each fixture. All you have vented is the main line.

    John
    Except for wet vents (and circuit vents and comb. drain/vent) which the horizontal becomes the vent....
    Matt
    Semi-professional plumbing designer
    Enjoying life in SW Florida

  5. #5
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Venting the washer with an AAV is a bad idea, because the washer is a pumped discharge...possible positive pressure...and the AAV can't deal with that!

  6. #6
    DIY Junior Member
    Join Date
    Dec 2009
    Location
    North Carolina
    Posts
    2

    Default thanks for the feedback

    The utility lav would use an AAV too. Is it possible to attach the washer before the toilet or is it best to attach it after the toilet? I can add non-AAV venting to the washer and the toilet without too much work. How close to the toilet do I need to have the vent? Can it not come out of the main line?

  7. #7
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,607

    Default vents

    for all practical purposes, you do NOT have ANY vents, at least none where they would perform their intended purposes. You have also created a "wasteful" system as far as the cost of installing it is concerned. DON'T listen to friends who do not know what they are talking about. You do not need that 3" line to the washing machine. IF you vent the system properly you will not get "gurgling". IF you do not vent it properly, it will gurgle regardless of where you connect it or what size pipe you use.