    What does the repair entail? Approx how much?

    Quote Originally Posted by Doherty Plumbing View Post
    I would agree especially if this furnace has the old style honeywell limit/fan switch.

  2. #17
    Journeyman & Gas Fitter Doherty Plumbing's Avatar
    Join Date
    Jun 2009
    Location
    Penticton, BC
    Posts
    810

    Default

    Quote Originally Posted by walds11 View Post
    What does the repair entail? Approx how much?
    The repair entails removing 4 screws, moving a couple of wires over to the new limit switch and then reattaching the 4 screws.

    If all goes well you can easily change one out in 30 mins.

    Take a picture of the front of the furnace for me ok.

    Cost? Less than $70 USD I would think... The part is about $70 CAD up here...

  3. #18
    DIY Member walds11's Avatar
    Join Date
    Nov 2009
    Location
    Philly, PA
    Posts
    61

    Default

    You mean pop the front panel off the furnace and take a pic of that?

    Quote Originally Posted by Doherty Plumbing View Post
    The repair entails removing 4 screws, moving a couple of wires over to the new limit switch and then reattaching the 4 screws.

    If all goes well you can easily change one out in 30 mins.

    Take a picture of the front of the furnace for me ok.

    Cost? Less than $70 USD I would think... The part is about $70 CAD up here...

  4. #19
    Journeyman & Gas Fitter Doherty Plumbing's Avatar
    Join Date
    Jun 2009
    Location
    Penticton, BC
    Posts
    810

    Default

    Quote Originally Posted by walds11 View Post
    You mean pop the front panel off the furnace and take a pic of that?
    Yes .........

  5. #20
    DIY Member walds11's Avatar
    Join Date
    Nov 2009
    Location
    Philly, PA
    Posts
    61

    Default

    This is the best I can do.
    Attached Images Attached Images   

  6. #21
    Journeyman & Gas Fitter Doherty Plumbing's Avatar
    Join Date
    Jun 2009
    Location
    Penticton, BC
    Posts
    810

    Default

    Quote Originally Posted by walds11 View Post
    This is the best I can do.
    Yes replace that limit control you took a close up of in the 2nd picture.

    All you have to do is basically wire the new one the exact same as that old one.

    On your old limit you'll notice that on the right side of it (when looking at it in the orientation it's in now) you'll see a brass jumper. It will either be intact or broken. Make sure you the new limit matches this. IE if it's broken break the one on your new one, and if it's not broken leave your new one alone.

    This jumper is used to determine if you have 120v or 24v controlling the circuit.

  7. #22
    DIY Member walds11's Avatar
    Join Date
    Nov 2009
    Location
    Philly, PA
    Posts
    61

    Default

    I must be blind, but where is the limit control? I don't see a brass jumper. My HVAC guy is coming over on Wednesday to install a hot water heater. I'll run it by him.

  8. #23
    Previous member
    Join Date
    Jul 2009
    Location
    North of the Mason dixon Line
    Posts
    1,150

    Default

    It's that thing with the circular disc and three black wires running into it and the cover off

  9. #24
    DIY Member walds11's Avatar
    Join Date
    Nov 2009
    Location
    Philly, PA
    Posts
    61

    Default

    Now I see it. Thanks!

  10. #25
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    Quote Originally Posted by walds11 View Post
    My HVAC systems are about 18-19 years old. Maybe no need to rush to replace the new systems even if I have to spend small amounts of money for mainatence and repair each year?
    I have a spreadsheet on my other computer that tells when to replace equipment. It's one of many equipment replacement strategies but this one does not take The Cost of Money into account.

    Now that I know how to post a "print screen" I'll try to find the thing and post it.
    With this and the expected lifetimes of equip. I think you can make a pretty rational and informed decision about replacements.