    Default Oil burner shut down problem Help!

    Hi there,

    I have a 3 years old Carlin oil burner installed on a OWB & OWT boiler. When the thermostat reach its set temperature and shut down the furnace, the oil burner will cycle on and off very rapidly 6 or 7 times at one second interval before stopping completely. it makes a sound like "rapid breathing". It doesn't feel normal to me. What may be the cause of it?

    Thanks in advance,

    JF

  2. #2
    Previous member
    Join Date
    Jul 2009
    Location
    North of the Mason dixon Line
    Posts
    1,150

    Default

    Probably the thermostat but could be the burner relay.

  3. #3

    Default

    I have experienced a similar problem on a Riello burner - it could be a bad burner control box.

  4. #4
    DIY Junior Member MAoilTech's Avatar
    Join Date
    Nov 2009
    Location
    MA
    Posts
    25

    Default

    Agree's with pete, aquiety, T-stat,Limit Control, or your Primary Control specially if you have R8184G type control (grey box with a red button) Contacts get worn out make the control click on and off rapidly run the unit and give the control few love taps and see if get stuck or shut off and on.