Thread: Furnace cycles while heating the home

  1. #1
    DIY Junior Member
    Join Date
    Dec 2009
    Location
    Utah
    Posts
    1

    Default Furnace cycles while heating the home

    I keep the heat at 65 degrees when I goto bed. When I wake up in the morning, I set it to 70 degrees. The furnace will come on, but it takes lots of breaks as it makes its way up to the newly set temperature. Because it takes so many breaks, it take forever for it to eventually reach 70 degrees. Here is some info I found on the controls that may be helpful to you smart guys:

    Lennox Elite Series
    Johnson Controls (G776RGD-14)
    .44 orifice
    Intermittent Pilot Ignition Control
    85 second trial
    15 second prepurge
    60 minute retry

    When the unit is taking a break, the fan is not blowing, but I hear the furnace still "on", whatever that means. On the Johnson Controls, I see a LED light that blinks 1 second on, 5 seconds off. According to the printed label on the controls:

    "in retry mode"

    The weird thing is, a "professional" said there was nothing wrong that he could see. Can someone help me figure out why the heater doesn't run continuously until the desired temperature is reached?

    Thanks!

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,382

    Default

    It sounds to me like the flame detector is shot. When a flame generated heating device turns the main burner on, it normally has a detector that determines the burner is actually burning. If it isn't, or it thinks it isn't, it will shut the gas off, then wait awhile for the unburned gas to 'purge' out of the chamber, then try again. Your system is not getting the signal that it actually lit. Could be dirty, could be out of position, could be bad, or the main board that signal goes to could have a bad receiver, and not see the good signal. Most common is a dirty sensor. There's often a way to test them, but you'd need the spec sheet or diagnostics and the proper tool (often a multimeter).

    Note, some burners have a maximum burn time, and will shut off, even if the set point isn't reached, for a few minutes before firing again. This is much longer than a few minutes, though, and wouldn't give an error code.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,607

    Default furnace

    You have to find out what is happening at that time. Normally, even if the burner goes out, the fan will continue to operate until the furnace is cooled down. So you have to know if the fan is off because the burner has not been operating, or what ever else the reason is. The burner will shut off if the thermostat is satisfied, the high limit switch is activated, or the burner flame has failed. Again, you have to determine the cause before any action can be taken.

  4. #4
    DIY Junior Member
    Join Date
    Dec 2009
    Location
    Texas
    Posts
    5

    Default

    Quote Originally Posted by nestman View Post
    I keep the heat at 65 degrees when I goto bed. When I wake up in the morning, I set it to 70 degrees. The furnace will come on, but it takes lots of breaks as it makes its way up to the newly set temperature. Because it takes so many breaks, it take forever for it to eventually reach 70 degrees. Here is some info I found on the controls that may be helpful to you smart guys:

    Lennox Elite Series
    Johnson Controls (G776RGD-14)
    .44 orifice
    Intermittent Pilot Ignition Control
    85 second trial
    15 second prepurge
    60 minute retry

    When the unit is taking a break, the fan is not blowing, but I hear the furnace still "on", whatever that means. On the Johnson Controls, I see a LED light that blinks 1 second on, 5 seconds off. According to the printed label on the controls:

    "in retry mode"

    The weird thing is, a "professional" said there was nothing wrong that he could see. Can someone help me figure out why the heater doesn't run continuously until the desired temperature is reached?

    Thanks!
    Did you find your answer? I'm having the same issue. Changed/cleaned several things but nothing worked. Tech couldnt figure it out either.

  5. #5
    Journeyman & Gas Fitter Doherty Plumbing's Avatar
    Join Date
    Jun 2009
    Location
    Penticton, BC
    Posts
    810

    Default

    Quote Originally Posted by john152 View Post
    Did you find your answer? I'm having the same issue. Changed/cleaned several things but nothing worked. Tech couldnt figure it out either.
    If you checked everything over and cleaned/changed the flame rod and nothing is seeming to help you probably need a new control board.

  6. #6
    Previous member
    Join Date
    Jul 2009
    Location
    North of the Mason dixon Line
    Posts
    1,150

    Default

    Quote Originally Posted by nestman View Post
    I keep the heat at 65 degrees when I goto bed. When I wake up in the morning, I set it to 70 degrees. The furnace will come on, but it takes lots of breaks as it makes its way up to the newly set temperature. Because it takes so many breaks, it take forever for it to eventually reach 70 degrees. Here is some info I found on the controls that may be helpful to you smart guys:

    Lennox Elite Series
    Johnson Controls (G776RGD-14)
    .44 orifice
    Intermittent Pilot Ignition Control
    85 second trial
    15 second prepurge
    60 minute retry

    When the unit is taking a break, the fan is not blowing, but I hear the furnace still "on", whatever that means. On the Johnson Controls, I see a LED light that blinks 1 second on, 5 seconds off. According to the printed label on the controls:

    "in retry mode"

    The weird thing is, a "professional" said there was nothing wrong that he could see. Can someone help me figure out why the heater doesn't run continuously until the desired temperature is reached?

    Thanks!
    It is normal. when the burner comes on it needs to heat up the exchanger to what ever the fan on speed is set at, then the fan comes on and blows for awhile and stops because it's bringing back cold air and cools off the exchanger, the burner either stays on or it may go off on high limit before the blower comes on again. It's real common when you set back the thermostat. You could change the high limit switch which is most likely the cause of the cycling but a lot of furnaces do that.

  7. #7
    Journeyman & Gas Fitter Doherty Plumbing's Avatar
    Join Date
    Jun 2009
    Location
    Penticton, BC
    Posts
    810

    Default

    Quote Originally Posted by Peter Griffin View Post
    It is normal. when the burner comes on it needs to heat up the exchanger to what ever the fan on speed is set at, then the fan comes on and blows for awhile and stops because it's bringing back cold air and cools off the exchanger, the burner either stays on or it may go off on high limit before the blower comes on again. It's real common when you set back the thermostat. You could change the high limit switch which is most likely the cause of the cycling but a lot of furnaces do that.
    It's not normal for a furnace's fan motor to cycle, after the furnace has fully started up, while the burner is still going. It should be the other way around with the blower going and the burner off.

    Nestman > I just read the manual for this furnance online and it's says it's a 2 stage furnace. Is it possible that maybe the furnace is cycling from hi to low fire and you're just not hearing the fan motor running while it's on low fire?

    What you need to do is run the furnace with the cover panel(s) off. There is probably a door switch on the fan compartment you'll need to tape closed. Ofcourse do ALL of this with the power OFF to the furnace. The fan motor is a dangerous thing. Once you are ready to watch the furnace run through a cycle turn the power back on to the furnace and watch it run through a cycle.

    This way you'll know for sure if the fan motor completely stops running or not.

    If the motor does stop completely while the burner is still going once the furnace is up and running (after initial startup) I would again say you need a new control board. These new furnaces are run by the control board and it tells the furnace to do everything it does basically. So if the fan is cycling on and off it's because the control board is telling it to cycle on and off. These newer furnaces rarely have heat switches like the older furnaces to bring the fan on and off. It's all controlled with timers and such built into the control board.

    I would suggest you phone technical support and talk to them too and see what they have to say about! They'll want you in front of the furnace with the model & serial #'s ready!

  8. #8
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    I'd say the duty cycle should be 100% until it reaches the setpoint temp. Then the duty cycle varies to maintain that temp.

  9. #9
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,382

    Default

    Most should run until the thermostat is satisfied. Every once in awhile, you'll find one that has a max run time timer and it will automatically turn off if it runs that long, but the on time is quite long, not a short cycle.

    It would be unusual to have the return air be cold enough to drop the heat exchanger temp low enough to have the fan turn off IMHO. If it did, the setting probably isn't optimum.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  10. #10
    Journeyman & Gas Fitter Doherty Plumbing's Avatar
    Join Date
    Jun 2009
    Location
    Penticton, BC
    Posts
    810

    Default

    Quote Originally Posted by jadnashua View Post
    It would be unusual to have the return air be cold enough to drop the heat exchanger temp low enough to have the fan turn off IMHO. If it did, the setting probably isn't optimum.
    This isn't even possible on a new furnace with a control board because like I said above they don't have heat switches to turn the fan on and off. It's all controlled through the board electronically.

  11. #11
    DIY Senior Member MG's Avatar
    Join Date
    Jun 2005
    Location
    Illinois - Near St. Louis
    Posts
    160

    Default

    I just replaced one of these ignition modules tonight. However, the flame sensor that they provide with it does not match the one I have. I cleaned up the one in there and it fired right up but its doing the same thing - cycling a lot. The new sensor is shorter than the old one and doesn't have the threaded fitting that the old one has. For now it's working though.
    Note: I am a DIY'er and not a professional. My posts here are observations / opinions and may or may not be in accordance with your local ordinances.

  12. #12
    DIY Senior Member MG's Avatar
    Join Date
    Jun 2005
    Location
    Illinois - Near St. Louis
    Posts
    160

    Default

    Followup - so far it's working fine and it appears that its working a lot because its doggone cold here this week.
    Note: I am a DIY'er and not a professional. My posts here are observations / opinions and may or may not be in accordance with your local ordinances.

  13. #13
    Journeyman & Gas Fitter Doherty Plumbing's Avatar
    Join Date
    Jun 2009
    Location
    Penticton, BC
    Posts
    810

    Default

    Quote Originally Posted by MG View Post
    Followup - so far it's working fine and it appears that its working a lot because its doggone cold here this week.
    Great. Glad it's up and running!

  14. #14
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,607

    Default cycling

    If the burner turns on and off, it is because the unit is heating faster than the fan can disperse the heat so it goes into high limit thermal shutdown. If the fan cycles on and off, it is because the burner cannot keep up with the demand, and the fan's LOW limit turns it off so you do not circulate "cool" air. It then starts up again when the temperature reaches the fan's turn on point.

  15. #15
    Journeyman & Gas Fitter Doherty Plumbing's Avatar
    Join Date
    Jun 2009
    Location
    Penticton, BC
    Posts
    810

    Default

    Quote Originally Posted by hj View Post
    If the burner turns on and off, it is because the unit is heating faster than the fan can disperse the heat so it goes into high limit thermal shutdown. If the fan cycles on and off, it is because the burner cannot keep up with the demand, and the fan's LOW limit turns it off so you do not circulate "cool" air. It then starts up again when the temperature reaches the fan's turn on point.
    On an older furnace yes, on a newer furnace no.

    On *most* newer furnaces the fans are not brought on and off based on temperature. They are usually brought on a certain amount of time after the burner has fired and should run until a certain amount of time after the burner has shut off. Again all of this is controlled through the control board.

    So if on a newer furnace you have a fan that is cycling on and off it's usually because the control board is shot. Notice I said usually :P