    Default Toilet flange not level

    Hello and thank you in advance for your help,

    I started a remodel of a bathroom and just finished lifting up the old floor (1" of mortar + thin ceramic tile over 5/8th plywood). The wood around the back part of the bowl was wet (not yet rotten, but wet about 1/2 way through) so I removed it.

    I started doing the math on how much more subfloor and cement board I would need (replacing the 1" mortar) and put a level on the flange to measure. It was not level. To make it level, I needed to lift it by almost 1/2 inch. (Also, still not sure if the flange should sit on the finished tile or even to it. Did not pay attention to the way it was before the demo. Would appreciate any help on that as well.)

    It did take some strength (mainly on my fingers) to get it to level. I looked at the hole in the joist (lucky I removed the wet wood to have access) and the PVC pipe was not hitting the top of the hole.

    It looks like the much of the stress (after it was leveled) would be on where the flange is attached to the PCV pipe. Actually, I can only see the flange and the pipe running through one joist, so I am not sure what is going on furter down the line.

    My question is how strong is the bond between the flange and the PVC pipe after they are glued together? Would I be safer to leave it unlevel (maybe just lift it 1/4" and shim the high side) and let the wax ring make up the difference? Pulling it half way up was less stress.

    Appreciate any advice.

  2. #2
    Plumber krow's Avatar
    Join Date
    Feb 2008
    Location
    Ontario, Canada
    Posts
    906

    Default

    Quote Originally Posted by prospectkid View Post
    My question is how strong is the bond between the flange and the PVC pipe after they are glued together? Would I be safer to leave it unlevel (maybe just lift it 1/4" and shim the high side) and let the wax ring make up the difference? Pulling it half way up was less stress.

    Appreciate any advice.
    It will not come apart.it will be a "solvent weld". You will find that the will be resiliant to most stresses. If you can pull the flange up with your hands, then the stress factor on the pipe and fittings should not be overwhelming.

    The flange should sit on the finished floor as a norm, but you can get away with the top surface of the flange with the top surface of your finished floor.

  3. #3
    DIY Senior Member dlarrivee's Avatar
    Join Date
    Jun 2009
    Location
    Canada
    Posts
    1,172

    Default

    Please elaborate on the drain going through a joist...?

  4. #4
    DIY Junior Member prospectkid's Avatar
    Join Date
    Nov 2009
    Location
    Prospect, KY
    Posts
    4

    Default

    Thank you for the reply. Really appreciate it. I was hoping that it would be like a metal weld as far as strength.

    Specific to the pipe running through the joists - The bathroom is on the second floor and I was referring to the floor joists that run 16" center. The waste pipe runs "through" the joist via a circular cutout. I think that you refer to these as joists. I am a weekend warrior, so please forgive me if my terminology is wrong.

    May I ask another question?:

    I need to make up 1” of sub floor (plywood and cement board) and tile. What do you recommend as far as the thickness of each and what height should you give the thin-set.

    I can do ¼” or ½” tile. Maybe greater than 1/4” tile – it is my kid’s bathroom and who knows that they will bring in – and drop.

    Again, really appreciate all your help.

  5. #5
    Plumber krow's Avatar
    Join Date
    Feb 2008
    Location
    Ontario, Canada
    Posts
    906

    Default

    I assume you already have an existing subfloor from the original build.
    I have used 3/8" plywood srewed down every 6" in the feild and 1/4 concrete board with a 3/8 tile in the past with no issues. Thickness of thin set will vary depending on the size of your floor tile . ie: 6x6, 8x8, 12x12 etc...

  6. #6
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,388

    Default

    More plywood is best. If you want to minimize the buildup, you could use Ditra from www.schluter.com - it's only 1/8" thick or so. The cement board (cbu) does nothing much to strengthen your floor, but plywood does.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014