    Cool Old Existing G.E. Circuit Breaker Panel

    Can and would you use QO SD Homeline circuit breaker in a G.E. panel.

    The panel has a 100 amp. main disconnect.

    The breakers in the G.E. panel are only going to be temporary, during the contruction
    stage.

    After which, a new panel will be installed in a new location, with the
    existing G.E. panels being remove.
    Last edited by Ford2001; 11-24-2009 at 06:57 PM.

  2. #2
    Network Engineer rmelo99's Avatar
    Join Date
    Jul 2006
    Location
    Connecticut
    Posts
    349

    Default

    Short answer is NO.

    That being said there are cross compatible breakers for some panels. Certain GE panels can take certain Cutler Hammer breakers.

    As far as SquareD is concerned even their QO and HOMELINE breakers aren't interchangable! What makes you think they would work in a GE panel?

  3. #3
    DIY Member Ford2001's Avatar
    Join Date
    Sep 2009
    Location
    Manchester, Vermont
    Posts
    32

    Cool Homeline breaker in a G.E. panel

    rmelo99 to your reply to my thread

    Didn't know, that why I put this thread in.

    Thanks for your answer. Now I know they will not work.