Light in crawl space

Users who are viewing this thread

Khayes

Member
Messages
56
Reaction score
0
Points
6
Location
Alpharetta, GA.
I want to install a single light in our crawl space with a switch near the access door. I want to tap into a line feeding a receptacle to the room just above the crawl space. The circuit is 20amp/#12Guage. Is it allowable to run a #14G leg off that circuit for the new light?
Thanks for any advice.
 
Last edited:

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
No, as I understand it. ANy wire up to the fixture must be sized for the protection device it is connected to (it can be larger, but not smaller). So, on that 20A circuit, you'd need to use 12g wire. There may be an exception...see what the pros have to say.
 

Billy_Bob

In the Trades
Messages
419
Reaction score
0
Points
0
Here is an official answer to that very question...
http://www.inspectorsjournal.com/Forum/topic.asp?TOPIC_ID=10538

And always best to ask your local electrical inspector. Local areas can modify the national rules as they see fit.

My personal opinion is that it is best to use all 12 ga. wire on a 20 amp circuit. (Be consistent in the wire size used for each circuit and that it be of the appropriate size for the breaker on that circuit.)
 

Cass

Plumber
Messages
5,947
Reaction score
7
Points
0
Location
Ohio
You can use a larger wire size than the breaker that is feeding the circuit but you can never use smaller...using smaller is a fire waiting to happen...
 