Want to run new feed to garage
Arfeller
Port Angeles, WA
I purchased my home about 2 year ago. The previous owner has used an exterior 12/2 with ground direct burrial cable to provide power to the garage.
I would like to add a 220V circuit and up the power to the garage.
I will abandon the 12/2 and run 6/3 with ground (romex, unless there is good reason to use single strand wires) in 2 1/2" conduit (underground). With a directly wired (No master) 100 amp 6 slot box mounted in the garage.
Total wire run length is ~60 feet (box to box including bends). Actual distance is about 45 feet.
I would use the 50 amp circuit in the house panel for the main.
In the box, i would have a 20amp 220v circut, and then two 110v circuits, 15 and 20 amp
So, if there are no problelms with this configuration, i do have a question about the grounding of the 100 amp box. The box comes with a grounding screw to connect the ground strip with the box. Do i use this?
Thank you
Alectrician
DIY Senior Member
1. No romex. Not rated for underground.
Use individual conductors. Black, black and white #8 and green #10 ground.
2. 2.5" conduit is way overkilled. 1" is plenty.
3. Neutral bus (white wires) is to be isolated from the enclosere. Do not install bond screw. Terminate grounds on a ground bar kit.
Also, install two 1/2" x 8' ground rods at least 6' apart and run a #6 wire to the ground bus.
Arfeller
Port Angeles, WA
1. Ok, good to know. This will save me on conduit also, I had chose 2 1/2" to get romex through.
3. If i ground the box with ground bar kit, then why do i need to run #10 ground from the house? What will that connect to if I ground the box to the
ground rods?
Ok, I looked into this some more and think I understand. I will bring the grounding wire from the house to the subpanel in the garage. I will connect this to the grounding bar and then connect the grounding bar to the grounding rods. However, this bar will not be connected to the neutral bar with the supplied bolt
Additionally, it sounds like my local code requires me to bring the feed into a 50 amp breaker (with a special bracket to secure in panel) to back feed the subpanel and create a shutoff
This will be used in alternative to the main lugs. Then the other breakers will be installed beside it.
And thank you for the reply!
Jar546
USA
www.inspectpa.com
Finally a poster with a brain that is not trying to get out of good advice or waiting for someone to tell them what they want to hear. Congrats
Tjbaudio
Las Vegas NV
#8 is too light for a 50A feed. I would go #6.
Arfeller
Port Angeles, WA
Thanks again for the input and help.
I have the ditch dug, conduit in, wire pulled, grounding rods pounded...
Only thing I forgot was the darn grounding kit. Need to pick one up for the subpanel to hook up the grounding rods and ground.
traffic626
Boston
If he's using conduit, why individual connectors instead of the underground rated wire? I'm asking because I have a 15A powering my garage and I was thinking of re-using the conduit to run a 30A panel.
Regarding the ground rods, are they required if you have them at the meter for the service coming in from the street?
Eddie
ActionDave
Electrician
Colorado
A better way to look at this is ask why would you use wire suitable for direct bury in conduit. Direct Burial rated wire can be in contact with the dirt, but if damaged you must redig to repair.
Ground rods are required at each structure.
