  1. #1

    Default Convert dryer vent to range hood vent?

    I recently replaced my gas dryer with an electric condensing washer/dryer combo unit so I have an external vent (3.5" vertical) in my apartment that I no longer use.

    Assuming it was appropriately cleaned could I use it to vent fumes from a range hood?

    I believe the current recirculating microwave hood (GE XL1800) can be adapted for external venting. I would need about 10ft of ducting with 3x 90 degree turns to reach the vent. Would an additional blower also be required somewhere?

    Just brainstorming...

    PG.

  2. #2
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Assuming your vent pipe is 4" diam. that is a little small for a range hood, but would be better than nothing.

  3. #3

    Default

    Yes, 4" metal duct. I'm on the top floor and travels what looks like 4-5 feet vertically through the roof.

    I found a PDF online for that suggests the hood is capable of handling up to 140ft of duct (with 10 feet deducted per 90 degree bend) but requires 6" diameter ducting. So I guess I'm stuffed.
    Last edited by petergunn; 11-08-2009 at 01:23 PM.

  4. #4
    Senior Robin Hood Guy Ian Gills's Avatar
    Join Date
    Jul 2007
    Location
    USA
    Posts
    2,781

    Default

    I'd be tempted to put a reducer on that, given that it's just a range hood.

    I'm stuck with carbon filters.

  5. #5
    DIY Senior Member Hube's Avatar
    Join Date
    Sep 2004
    Location
    Ontario
    Posts
    156

    Default

    Quote Originally Posted by Ian Gills View Post
    I'd be tempted to put a reducer on that, given that it's just a range hood.

    I'm stuck with carbon filters.
    huh!!! Why on earth would you suggest putting a REDUCER on a vent that already is not as large as it should be???

    actually in my opinion, this 4" vent could do ok to some satisfaction depending on the size of the fan that will exhaust this range hood air.

  6. #6
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Quote Originally Posted by Hube View Post
    huh!!! Why on earth would you suggest putting a REDUCER on a vent that already is not as large as it should be???

    actually in my opinion, this 4" vent could do ok to some satisfaction depending on the size of the fan that will exhaust this range hood air.

    I think he just means a reducer to match the outlet of the hood to the 4" duct.

    I agree that exhausting through the 4" is preferable to his current non-vented situation. It may be a little loud, and not move as much air as designed, but I still think better than not.

  7. #7
    In the Trades Gary Swart's Avatar
    Join Date
    Sep 2004
    Location
    Yakima WA
    Posts
    7,246

    Default

    How hard would it be to enlarge the hole(s) where the 4" vent is and put in a 6"?

  8. #8
    Homeowner geniescience's Avatar
    Join Date
    Nov 2005
    Location
    humid summers hot, humid winters cold
    Posts
    2,152

    Default

    Quote Originally Posted by petergunn View Post
    ... apartment .... microwave hood (GE XL1800) .... 10ft of ducting with 3x 90 degree turns to reach the vent. Would an additional blower also be required somewhere?
    1. Never add "an additional blower "
    2. "Apartment" = tell your landlord everything
    3. Ten feet and three elbows and a 4" duct = an insufficient flow; you will not be satisfied OR you will have had some fun trying something out; the next occupant after you will not be satisfied.

    Brainstorming is good. Be sure about what you later implement.

  9. #9
    Homeowner geniescience's Avatar
    Join Date
    Nov 2005
    Location
    humid summers hot, humid winters cold
    Posts
    2,152

    Default

    Quote Originally Posted by geniescience View Post
    2. "Apartment" = tell your landlord everything
    Code does not allow mixing/combining kitchen exhaust vents and dryer vents, in buildings of a certain size -- which you as an apartment dweller may be living in. Most likely. I don't know what size building it starts at.

  10. #10
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,412

    Default

    While you may no longer need the dryer vent, the next occupant of the apartment may, so it's not a good idea to retask it. even though the filters on the range hood trap most of the grease, they still let a little through. The more elbows, the more chances of that grease accumulating. Grease is worse than lint, and a grease fire is a possibility. If I was the landlord, I'd not approve that. Now, depending on where a new vent might be put, I might consider venting the range hood out on a shorter, more direct path, especially if the tenant was willing to pay for it.

    Some things can be done in your own home, but an apartment is much more restrictive. It's generally, what you see is what you get.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  11. #11
    I&C Engineer (mostly WWTP) Lakee911's Avatar
    Join Date
    Aug 2005
    Location
    Columbus, OH
    Posts
    1,328

    Default

    Not to mention the next tenant's lint is going to stick to the grease and it will be a mess (if it doesn't catch on fire).